    <p>Adnan Rasheed,</p>
    <p>  There are two methods that you can follow. One is to modify
      your Excel data so that it complies with the Type99 "user defined"
      format. The other is to use Type9 to read the Excel format that
      you already have and then to set up a Type16 (radiation processor)
      to process the raw solar radiation from your data file. Please
      refer to the Type99 and Type9 sections of the
      04-MathematicalReference manual for information on how to set up
      the Types. There are also examples that use both Type99 and Type9
      in the ..\Trnsys17\Examples\ directory. One hint: if you're using
      Type9 you'll want to save a copy of your Excel spreadsheet in
      either a comma separated value (*.csv) or a tab delimited text
      format.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 06/19/2016 04:18, adnan rasheed via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAG9tXZh02HpG=KGiFVe0DuxMs1P4u5G-CO6pDVHmczjMc6AQGg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello everyone,
        <div><br>
        </div>
        <div>i have weather data file in excel format (measured data) .
          i want to use it in my simulation what TYPE of TRNSYS weather
          data reader  i can use and how to prepare weather data file
          which is readable by TRNSYS . how can TRNSYS will identify
          this is temperature and this is wind speed i am confused about
          tha . can anybody send me an example of the self prepared
          weather data file..</div>
        <div><br>
        </div>
        <div>thanks</div>
        <div>Adnan Rasheed</div>
        <div>PhD student</div>
        <div>KyungPook National University, south Korea  </div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Fri, Jun 17, 2016 at 12:40 AM, Tuule
          Mall Kull via TRNSYS-users <span dir="ltr"><<a
              moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org"
              target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a></a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">
              <div>
                <div>
                  <div>Dear all,<br>
                    <br>
                  </div>
                  As a special case I am trying to simulate a building
                  with periodic boundary conditions with a period of one
                  day. I generated the periodic artificial weather data
                  file and i am using the user format (Type99). However,
                  I need to set a constant date so that the beam
                  radiation values would not change from day to day. How
                  could i do that?<br>
                  <br>
                </div>
                Best regard,<br>
              </div>
              Tuule Mall Kull<br>
              <div>
                <div><br>
                </div>
                <div>Institute of Building Research and Innovation<br>
                </div>
                <div>Vienna, Austria<br>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            TRNSYS-users mailing list<br>
            <a moz-do-not-send="true"
              href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br>
            <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>