    Massimo,<br>
      Assuming that you have a 1-year weather data file the best way to
    accomplish that is to set your simulation start time to an hour of
    the year near the end of december (8592, for example will set the
    simulation start time to one week before the end of december). You
    then set your simulation stop time to 17520. If you think that you
    need a longer warmup period (for instance if you are doing a
    building and ground coupling then you can simply run a multi year
    simulation (start time 0, end time 17520 26289, etc.)<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 04/27/2016 08:21, massimo truant
      wrote:<br>
    </div>
    <blockquote cite="mid:5720bccb.0e711c0a.48265.0f0a@mx.google.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 2.0cm 2.0cm 2.0cm;}
div.WordSection1
        {page:WordSection1;}
--></style>
      <div class="WordSection1">
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Good afternoon,</p>
        <p class="MsoNormal">My question is very simple: is possible to
          assign to trnsys a period of time of pre-simulation before the
          real simulation (just to fix the data of the iteration)?</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks to all</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Inviato da <a moz-do-not-send="true"
            href="https://go.microsoft.com/fwlink/?LinkId=550986">Posta</a>
          per Windows 10</p>
        <p class="MsoNormal"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif"><o:p> </o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>