Massimo,<br>
Make sure that you are using a small enough timestep (1-5 minutes
is usually best). Type2 can only make one control decision per time
step and if your timestep is too long then controllers either cannot
converge on a decision or they don't do a good job of maintaining
the setpoint. You might also look at Type108. It sounds as though
you have set up Type2 properly but Type108 offers a somewhat more
intuitive thermostat model. You can disable stages 2 and 3 by
setting very high (or low, as appropriate) setpoints for those
stages.<br>
kind regards,<br>
David<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 04/27/2016 11:39, massimo truant
wrote:<br>
</div>
<blockquote cite="mid:5720eb3c.81da1c0a.6564a.6bdb@mx.google.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:#954F72;
text-decoration:underline;}
.MsoChpDefault
{mso-style-type:export-only;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:70.85pt 2.0cm 2.0cm 2.0cm;}
div.WordSection1
{page:WordSection1;}
--></style>
<div class="WordSection1">
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Good afternoon,</p>
<p class="MsoNormal">I have a problem with type 2d. I use it
like a thermostat but it doesnt work always. In my project
type 2d activates a ventilation system when the difference
between imput 1 and imput 2 is less than 2°C and it has to
stop the system when that difference is less than -2.</p>
<p class="MsoNormal">Example</p>
<p class="MsoNormal">25° is the temperature that I want</p>
<p class="MsoNormal">The system should be activated when
temperature reaches 27°C and should stop its action when the
temperature reaches 23°C.</p>
<p class="MsoNormal">But it doesn’t work sometimes the system is
activated when the temperature is near 26°C and it is stopped
when the temperature is near 24.</p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Someone knows the reason of that?</p>
<p class="MsoNormal">Thanks to all</p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Inviato da <a moz-do-not-send="true"
href="https://go.microsoft.com/fwlink/?LinkId=550986">Posta</a>
per Windows 10</p>
<p class="MsoNormal"><span
style="font-size:12.0pt;font-family:"Times New
Roman",serif"><o:p> </o:p></span></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>