    Muthalagappan Narayanan,<br>
      Type539 contains a control mode input that allows it to internally
    compute the flow rate required in order to achieve a desired outlet
    temperature. The desired flow rate can then be passed to an equation
    to turn it into a control signal to be passed to the pump that is
    actually delivering the flow to the collector. This way the
    collector gets the flow that it needs in order to maintain the
    desired outlet temperature. If I am mistaken in understanding what
    you are trying to do, please let me know.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 04/12/2016 09:47, Muthalagappan
      Narayanan wrote:<br>
    </div>
    <blockquote
cite="mid:CAOMBxbROzmRJLkucgdYyVu0qtCZ8qXKZ3sx2VvM7U0tU=GcwAw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello all,
        <div><br>
        </div>
        <div>I am simulating a solar thermal system and we would like to
          have a matched flow control strategy. For this, I tried with
          type 539 collector and also with type 23 PID, but anyway I
          could not achieve it. When I use PID, the set point is being
          checked with the collector outlet temperature and the control
          signal is sent to the variable pump and during the simulation
          I only see repeated oscillations between minimum and maximum
          control signal value. I just PI controller and I tried almost
          all the possibilities, I know. It would be great if someone
          has already implemented matched flow control for the collector
          and could help me out for a solution or share their ideas.
          Thanks</div>
        <div><br>
        </div>
        <div>With Regards</div>
        <div>Muthalagappan Narayanan</div>
        <div>Hochschule Ulm, Germany</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>