<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Ravindra,<br>
      The answer to your question depends somewhat on which models you
    are talking about. Most TRNSYS models assume that the fluid
    properties (usually density and specific heat) are constant over the
    temperature range that they will experience during the simulation.
    The assumption goes all the way in to the derivation of the
    equations used in the model. If you need a piece of equipment whose
    working fluid's properties must change with temperature then you
    have to rederive the basic equations and rewrite or revise the
    model. There are some models in the TESS High Temperature Solar
    library that allow you to enter coefficients that describe how the
    properties of the working fluid vary with temperature.<br>
    kind regards,<br>
     David<br>
       <br>
    <br>
    <div class="moz-cite-prefix">On 03/15/2016 07:36, v ravindra wrote:<br>
    </div>
    <blockquote
cite="mid:CADb1Z3J3cXot_ZWRNeYzmoHqXeYcmz9ts1OWo_J1w4WKckL=tg@mail.gmail.com"
      type="cite">
      <div dir="ltr">In a solar domestic hot water system is it possible
        to change the properties of the working fluid. I mean the water
        will be heated but the secondary fluid is changed. I want to use
        supercritical CO2 as the working fluid. Please guide me in this
        thing.
        <div> 
          <div>
            <div>
              <div class="gmail_signature">
                <div dir="ltr">
                  <div dir="ltr">V.Ravindra<br>
                    <br>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>