<span style="font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255);">David Sir,</span><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;"><br></div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">Thank you very much for your positive and prompt response. I need some more clarifications in this regard.</div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;"><br></div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">I've a collector <b><font color="#0000ff">whose hot water drain should be started only if outlet temperature is above 50 degree Celsius</font></b> by switching <b><font color="#0000ff">ON</font></b> the pump.<br><br>Kindly guide me on connections as per attached image.</div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;"><br></div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">Thanks a lot.</div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;"><br></div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">Regards</div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;"><br></div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">Veekay</div><div style="position: static; font-family: sans-serif; font-size: 14px; background-color: rgb(255, 255, 255); background-repeat: no-repeat;">India </div><br>From: David BRADLEY <d.bradley@tess-inc.com><br>Sent: Thu, 17 Dec 2015 03:05:05 <br>To: "TRNSYS users mailing list at OneBuilding.org" <trnsys-users@lists.onebuilding.org>, vviinnoodd@rediffmail.com<br>Subject: Re: [TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.<br>
Veekay,<br>
There are two ways that Type2 can be used. Most commonly it is
used as a differential controller such that it turns on when the
difference between two temperatures exceeds a certain amount and
then stays on until the difference between those temperatures falls
to a different amount. You'd use this in a solar thermal system when
you want to turn on the collector if the collector temperature
exceeds the storage tank temperature by (for example) 10C no matter
what the temperature of the storage tank. This was the method that
Alastair correctly suggested.<br>
You can also use Type2 like a more traditional thermostat in which
case you typically want to turn on a device when a monitored
temperature exceeds (or falls below) a certain set point value.
There are proformas for Type2 set up to do this. They are located in
Controllers: Aquastat: Heating Mode and Controllers: Aquastat:
Cooling Mode. Alternatively you can use Type108 which, while it
allows for more than one stage of control, can also be used as a
simple thermostat in either heating or cooling mode.<br>
kind regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 12/16/2015 12:44, Vinod wrote:<br>
</div>
<blockquote cite="mid:<a href=" javascript:void(0);"="" onclick="top.ajaxMail.ext.switchTo('@Compose','mode=mail_to_individual&email=20151216184430.5581.qmail@f4mail-235-223.rediffmail.com');">20151216184430.5581.qmail@f4mail-235-223.rediffmail.com"
type="cite">Please help me in TRNSYS 17: How to connect a
thermostat switch (Type 2b) to switch ON a pump at a particular
temperature range else keep the pump OFF.
<div><br>
</div>
<div>My purpose is to run the pump to discharge after achieving a
particular temperature.</div>
<div><br>
</div>
<div>Thanks</div>
<div><br>
</div>
<div>Veekay</div>
<div>India</div>
<br>
<a href='https://sigads.rediff.com/RealMedia/ads/click_nx.ads/www.rediffmail.com/signatureline.htm@Middle?'><img moz-do-not-send="true" src="https://sigads.rediff.com/RealMedia/ads/adstream_nx.ads/www.rediffmail.com/signatureline.htm@Middle></a>
<table cellpadding="0" cellspacing="0">
<tbody>
<tr>
<td>
<div style="font-family: Arial, Helvetica, sans-serif;
font-size:14px">Get your own <span style="padding-bottom: 0px; background-color: #cc0000;
padding-left: 3px; padding-RIGHT: 3px; font-family:
Arial, Helvetica, sans-serif; color: #ffffff;
font-size: 12px; padding-top: 0px"><b>FREE</b></span>
website, <span style="padding-bottom: 0px;
background-color: #c00; padding-left: 3px;
padding-RIGHT: 3px; font-family: Arial, Helvetica,
sans-serif; color: #ffffff; font-size: 12px;
padding-top: 0px"><b>FREE</b></span> domain & <span style="padding-bottom: 0px; background-color: #c00;
padding-left: 3px; padding-RIGHT: 3px; font-family:
Arial, Helvetica, sans-serif; color: #ffffff;
font-size: 12px; padding-top: 0px"><b>FREE</b></span>
mobile app with Company email. </div>
</td>
<td><a moz-do-not-send="true" href="//www.rediffmail.com/cgi-bin/red.cgi?red=http%3A%2F%2Ftrack%2Erediff%2Ecom%2Fclick%3Furl%3D%5F%5F%5Fhttp%3A%2F%2Fbusinessemail%2Erediff%2Ecom%3Fsc%5Fcid%3Dsign%2D1%2D10%2D13%5F%5F%5F%26amp%3Bcmp%3Dhost%26amp%3Blnk%3Dsign%2D1%2D10%2D13%26amp%3Bnsrv1%3Dhost&isImage=0&BlockImage=0&rediffng=0&rogue=387537254f7eee557c3b17544bd037e8098bd82e" style="font-family: Arial, Helvetica, sans-serif; color:
#fff; font-size: 14px; color:#0000cc" target="_blank" rel="external"><b>Know
More ></b></a><!-- <in-put type="button" cl-ass="button" on-click="parent.location='http://track.rediff.com/click?url=___http://businessemail.rediff.com/company-email-hosting-services?sc_cid=signature-23-9-13___&cmp=signature-23-9-13&lnk=mypagelogout&nsrv1=host'" value="Know more >"> </input> --></td>
</tr>
</tbody>
</table>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
<a href='http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org'>http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+<a href='http://1.608.274.257'>1.608.274.257</a>7
F:+<a href='http://1.608.278.147'>1.608.278.147</a>5
d.bradley@tess-inc.com
<a href='http://www.tess-inc.com'>http://www.tess-inc.com</a>
<a href='http://www.trnsys.com'>http://www.trnsys.com</a></pre>
<br><A HREF="https://sigads.rediff.com/RealMedia/ads/click_nx.ads/www.rediffmail.com/signatureline.htm@Middle?" target="_blank"><IMG SRC="https://sigads.rediff.com/RealMedia/ads/adstream_nx.ads/www.rediffmail.com/signatureline.htm@Middle"></A><table cellpadding="0" cellspacing="0"><tbody><tr><td><div style="font-family: Arial, Helvetica, sans-serif; font-size:14px">Get your own <span style="padding-bottom: 0px; background-color: #cc0000; padding-left: 3px; padding-RIGHT: 3px; font-family: Arial, Helvetica, sans-serif; color: #ffffff; font-size: 12px; padding-top: 0px"><b>FREE</b></span> website, <span style="padding-bottom: 0px; background-color: #c00; padding-left: 3px; padding-RIGHT: 3px; font-family: Arial, Helvetica, sans-serif; color: #ffffff; font-size: 12px; padding-top: 0px"><b>FREE</b></span> domain & <span style="padding-bottom: 0px; background-color: #c00; padding-left: 3px; padding-RIGHT: 3px; font-family: Arial, Helvetica, sans-serif; color: #ffffff; font-size: 12px; padding-top: 0px"><b>FREE</b></span> mobile app with Company email. </div></td><td><a href="http://track.rediff.com/click?url=___http://businessemail.rediff.com?sc_cid=sign-1-10-13___&cmp=host&lnk=sign-1-10-13&nsrv1=host" style="font-family: Arial, Helvetica, sans-serif; color: #fff; font-size: 14px; color:#0000cc" target="_blank"><b>Know More ></b></a><!-- <in-put type="button" cl-ass="button" on-click="parent.location='http://track.rediff.com/click?url=___http://businessemail.rediff.com/company-email-hosting-services?sc_cid=signature-23-9-13___&cmp=signature-23-9-13&lnk=mypagelogout&nsrv1=host'" value="Know more >"> </input> --></td></tr></tbody></table>