<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Wajahat Khan,<br>
      Both of those components base their estimate of performance on a
    performance map that gives (essentially) device capacity and COP as
    a function of the current inlet conditions. The refrigerant and
    indeed all the inner workings of the device are irrelevant because
    their properties are built in to the performance map. It is
    recommended that you find a performance map for the specific
    equipment that you are trying to model if at all possible. Such data
    can often be obtained from manufacturers in their published
    literature. <br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/22/2015 09:58, wajahat Khan
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAFzjgiBg0cxf4VtMiuYoZsEmgQYgKpwPDBe3vYUiixOXsqEj6w@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default" style="color:#ff00ff">My question is
          regarding Adsorption chiller type 909 and absorption chiller
          type 107.</div>
        <div class="gmail_default" style="color:#ff00ff"><br>
        </div>
        <div class="gmail_default" style="color:#ff00ff">Both of these
          chillers have external files for different parameters but
          there is no information about the refrigerant absorbent pair
          in case of absorption chiller ie which refrigerant absorbent
          pair is used.Similarly i didnt find any information about
          refrigerant adsorbent pair used in adsorption chiller.No
          information available that data available in external files is
          for which pair?</div>
        <div class="gmail_default" style="color:#ff00ff">Any have idea
          about this? </div>
        <div><br>
        </div>
        -- <br>
        <div class="gmail_signature">
          <div dir="ltr">
            <div>
              <div><b>Engr M Wajahat Khan<br>
                </b></div>
              <b>MS Mechanical<br>
              </b></div>
            <div><b>Cryogenic Engineer</b><br>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>