    Safwan,<br>
      Most of the HVAC equipment models include an output that will tell
    you how much energy they transferred to their air (or water) stream
    and also how much power they consumed. It sounds as though your
    model makes some use of the TRNBuild automatic heating and cooling
    types to calculate space load and some use of HVAC equipment to
    compute energy consumption. I would not recommend such a method. I
    would recommend that you disable the automatic heating and cooling
    in TRNBuild to allow the zone temperatures to float. You then
    implement thermostat models in the Studio to watch the zone
    temperature and command the HVAC equipment to turn ON and OFF
    appropriately so as to maintain your desired temperature in the
    zones of the building.<br>
    regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 09/21/2015 07:16, safone samsuddin
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1602879273.887441.1442837787386.JavaMail.yahoo@mail.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:times
        new roman, new york, times, serif;font-size:12px">
        <div id="yui_3_16_0_1_1442837324270_2340">Hi Everyone,</div>
        <div id="yui_3_16_0_1_1442837324270_2340"><br>
        </div>
        <div id="yui_3_16_0_1_1442837324270_2340">Does anybody know how
          to calculate HVAC power consumption such as Heat Pump and
          using Radiator as heating emitter in Type 56 multizone
          building?</div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">Do I need to
          set the heating ON in TRNSBUILD for each zones with the
          setpoint temperature? </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">I've
          simulate 2 scenarios with Heating ON and off using radiant
          heat transfer into zones. When the Heating ON, the TAIR
          trending of the zones will try to follow the setpoint. </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">However,
          when HEATING is OFF, the temperature TAIR and Toperative will
          follow according Thermostat setpoint, however, it always
          overheating when sun radiation gave extra heating into the
          Type 56 house.</div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">Anyone can
          suggest me, what would be the best solution to calculate
          energy consumption and heat gain of the zone? </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">Regards</div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1442837324270_2340" dir="ltr">Safwan</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>