<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <span style="color: black;"><span style="color: black; line-height:
        115%; font-family: "Calibri","sans-serif";
        font-size: 11pt;" lang="EN">Zhuo Li,<br>
         Without seeing your project files, it is not possible to
        determine the cause of the unrealistically high temperatures. I
        would recommend that you send your project files to your
        distributor's technical support hotline for assistance. <br>
        <br>
          The warnings that you are receiving may well be related to the
        high temperatures. Performance maps in TRNSYS usually contain
        data for a range of inlet conditions. For example the samp_c.dat
        file contains performance data for chillers whose return chilled
        water temperatures are between 4.4C and 10C. If the water
        returning to the chiller is above 10C then the performance data
        returned from the map may not be valid. If the problem happens
        only a few times during the simulation then it can usually be
        ignored. If the situation arises often then either the system
        configuration or the data file need to be changed so that valid
        performance data is returned.<br>
        <br>
        kind regards,<br>
         David<br>
        <br>
      </span></span><br>
    <div class="moz-cite-prefix">On 09/14/2015 01:00, Zhuo Li wrote:<br>
    </div>
    <blockquote
cite="mid:CY1PR0701MB20091CF201BD7F2C0E7B0BE5DB5D0@CY1PR0701MB2009.namprd07.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
      <div id="divtagdefaultwrapper" style="color: rgb(0, 0, 0);
        font-family: Calibri,Arial,Helvetica,sans-serif; font-size:
        12pt; background-color: rgb(255, 255, 255);">
        <p><span style="color: black;">Dear Trnsys users,</span></p>
        <p><span style="color: black;"></span> </p>
        <p><span style="color: black;">I am using type 56 to model an
            air conditioning system for a three-story building.
          </span><span style="color: black;" lang="EN">In my program,
            each floor has an air handling unit and the external air
            relative humidity ratio</span><span style="color: black;">,</span><span
            style="color: black;" lang="EN"> mass flow rate, and
            temperature are obtained as ventilation inputs to building
            model from Type 607</span><span style="color: black;">,
            which is connected to cooling coils (type 508).<span> 
            </span>The temperatures of thermal zones of 1st floor are
            within acceptable range, whereas temperatures of thermal
            zones of 2nd and 3rd floor are going infinitely high. How
            can I solve this problem?</span></p>
        <p><span style="color: black;"></span> </p>
        <span style="color: black;">
          <p><span style="color: black;">In addition, I encountered
              problems with chiller and ducts.
            </span><span style="color: black;" lang="EN">The warning
              messages are written below:</span></p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            0pt; line-height: normal;">
            <span style="color: black;" lang="EN"></span> </p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            0pt; line-height: normal;">
            <span style="color: black;">1) The file\Trnsys 17\Tess
              Models\SampleCatalogData\AirCooledChiller\Samp_C.dat was
              called with a first independent variable value below the
              range supplied in the data file. Data is interpolated
              within the data file range but is not extrapolated beyond<span> 
              </span>the range. Performance of the equipment modeled by
              this unit may be incorrect.</span></p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            0pt; line-height: normal;">
            <span style="color: black;" lang="EN">2) The referenced
              UNIT\ (Type 607)\ has called the PSYCHROMETRICS routine
              with a humidity ratio above the saturation humidity ratio
              for the given dry bulb temperature. The air was assumed
              saturated at the given dry bulb temperature and the
              humidity ratio set for this condition.</span><span
              style="color: black;"></span></p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            10pt; line-height: normal;">
            <span style="color: black;">For the chiller, parameter of
              rated capacity was changed and other parameters remained
              as default values.</span></p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            10pt; line-height: normal;">
            <span style="color: black;"></span><span style="color:
              black;" lang="EN">Thanks in advance for your help.</span></p>
          <p class="MsoNormal" style="background: white; margin: 0in 0in
            10pt; line-height: normal;">
            <span style="color: black;" lang="EN">B</span><span
              style="color: black;" lang="EN">est regards,</span><span
              style="color: black; font-size: 14pt;"></span></p>
          <p><span style="color: black; line-height: 115%; font-family:
              "Calibri","sans-serif"; font-size:
              11pt;" lang="EN">Zhuo Li</span></p>
        </span>
        <p><span style="color: black;"></span> </p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>