<div dir="ltr">With Trnsys everything is possible. The drawback is the time it takes. Reporting needs to be setup for a lot of outputs (hours load not met amoungst others). One of the things I find very "rough" is that there is no "auto-sizing". You'll need to manually "auto-size" all componants of the system.<br></div><div class="gmail_extra"><br><div class="gmail_quote">2015-09-03 16:11 GMT+02:00 David BRADLEY <span dir="ltr"><<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Filippo,<br>
  Simulating the 90.1 Appendix G baseline systems almost always involves the use of multiple Types. If you have questions about a particular baseline system, please tell me which one and I can probably give you some guidance. For the most part the TESS HVAC library contains the components that you would need. We do have a VAV air handler component that I have used for LEED simulations although it is not officially part of either the standard library or the TESS Libraries.<br>
<br>
  As far as the files that you need to submit along with your LEED forms, in my experience this is a bit of a guessing game between you and the reviewer. TRNSYS does not have the kind of standardized forms that LEED reviewers are used to. I usually submit the *.dck and the *.b17. In general I use a Type46 (printegrator) to generate one or more output files the contain the monthly power draw of all the active components of the systems (fans, pumps, compressors, heaters, etc.). I then put the contents of those files into a spreadsheet that I submit to the reviewer.<br>
kind regards,<br>
 David<br>
<br>
<br>
On 09/01/2015 04:05, Filippo Busato wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi everybody,<br>
        has anyone experience LEED simulation in TRNSYS 17?<br>
<br>
I have two questions:<br>
1. is there any specific type developed, or a guideline, to simulate HVAC plant according to appendix G ASHRAE 90.1;<br>
2. what are the files that needs to be attached to the LEED PI form? Is there any type or procedure guide to print the correct forms?<br>
<br>
Thanks<br>
Filippo Busato - PhD<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
<br>
</blockquote>
<br>
-- <br>
***************************<br>
David BRADLEY<br>
Principal<br>
Thermal Energy Systems Specialists, LLC<br>
22 North Carroll Street - suite 370<br>
Madison, WI  53703 USA<br>
<br>
P:<a href="tel:%2B1.608.274.2577" value="+16082742577" target="_blank">+1.608.274.2577</a><br>
F:<a href="tel:%2B1.608.278.1475" value="+16082781475" target="_blank">+1.608.278.1475</a><br>
<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a><br>
<br>
<a href="http://www.tess-inc.com" rel="noreferrer" target="_blank">http://www.tess-inc.com</a><br>
<a href="http://www.trnsys.com" rel="noreferrer" target="_blank">http://www.trnsys.com</a><br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
</blockquote></div><br></div>