<html>
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
</head>
<body dir="ltr">
<div id="divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#FFFFFF;font-family:Calibri,Arial,Helvetica,sans-serif;">
<p>Dear David.</p>
<p>Did you active the heating and the infiltration types of your building?, as indicated in the manual. It is not clear from your last part of the mail (the note).</p>
<p>The approach behind this calculation is very simple, TRNBUILD is looking for a sort of steady state calculation of your building using a transient tool, then an entire month is simulated (a large cold night of 31 days) with the mínimum temperature maintained
 at all times, this way even a very massive Wall will forget the initial conditions (initial temperaturas of the layers).</p>
<p>Regards.</p>
<p><br>
</p>
<div style="color: rgb(0, 0, 0);">
<hr tabindex="-1" style="width: 98%; display: inline-block;">
<div id="divRplyFwdMsg" dir="ltr"><font color="#000000" face="Calibri, sans-serif" style="font-size: 11pt;"><b>De:</b> TRNSYS-users <trnsys-users-bounces@lists.onebuilding.org> en nombre de David Geiger <david-geiger@web.de><br>
<b>Enviado:</b> jueves, 2 de julio de 2015 15:19<br>
<b>Para:</b> trnsys-users@lists.onebuilding.org<br>
<b>Asunto:</b> [TRNSYS-users] [TRNBuild] max heat load calulation</font>
<div> </div>
</div>
<div>
<div style="font-family: Verdana; font-size: 12px;">
<div>Dear all,</div>
<div> </div>
<div>I would like to use the function "max heat load calculation" in TNRBuild for a fast comparison</div>
<div>with my manual calculations using the DIN guidelines.</div>
<div> </div>
<div>The usage of the function itself is not the problem, as that is well explained in the manual.</div>
<div>My questions arise after I hit "Run TRNSYS". The simulation time is 744 h and results in</div>
<div>heat loads varying from 6.07 kW to 0.22 kW which leads to the following questions:</div>
<div> </div>
<div>-What is the correct value for the max load or how do I obtain it using the plotted graph or the printed data?</div>
<div>-It seems there is a short attack phase at the beginning, is the max value the first one after the system stabilizes or just the overall highest value?</div>
<div>-What is the general approach behind the calculation or why is there a varying result at all, since (as far as I understand it from the manual) all variables are fixed and hence there should only be a single result?</div>
<div> </div>
<div>As a potentially important side note: The building was created using the wizard for multizone buildings,</div>
<div>with the default options and thus contains the predefined configurations such as "no heating", "no cooling", "no (natural) ventilation" and the LEAKY infiltration type. The initial room temperature is 20°C an it is just a single zone.</div>
<div> </div>
<div>Thanks in advance!</div>
<div> </div>
<div>Regards,</div>
<div>David</div>
</div>
</div>
</div>
</div>
</body>
</html>