<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Salima Adjiri,<br>
      To clarify in case I do not entirely understand your question
    typical absorption chillers have a refrigerant that is entirely
    internal to the machine and then they have water as a working fluid
    in their cooling liquid, chilled liquid and hot liquid loops. I am
    not certain whether you are asking about how to change the assumed
    refrigerant in Type107 or if you are intending to change the working
    fluid in the heat exchange loops. <br>
    <br>
      The type of refrigerant inside the machine gets wrapped up into
    the performance data files that describe the machine's cooling
    capacity as a function of the heat exchanger loop inlet conditions.
    I suppose that if you had such data for a machine that used ammonia
    as its refrigerant then you could reasonably model an ammonia based
    hot-water fired chiller with it.<br>
    <br>
      The difficulty with changing the working fluid in the cooling
    loop, heating loop, or chilled loop to ammonia is that ammonia
    properties are not very constant over the temperature range that you
    would likely be working with. Type107 (and nearly all other TRNSYS
    components) assume that specific heat and density of the working
    liquid is constant so you have to be careful which fluids you
    specify.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 5/7/2015 5:18 AM, salima adjiri
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAMDA00ufGBALPJoZ+NKda6OZ8Jrm8Z7mvX-K=heNkJLF24EtBA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi,
        <div>I want to know if we can change proprities of coolling
          fluid in type107. </div>
        <div>we want to replace water by ammonia.</div>
        <div><span style="font-size:12.8000001907349px">kind regards,</span><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>