<html>
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
</head>
<body dir="ltr">
<div id="divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#FFFFFF;font-family:Calibri,Arial,Helvetica,sans-serif;">
<p>David,<br>
</p>
<p><br>
</p>
<p>Thank you. Yes,I am trying to achieve an outlet temperature set at 8th input and I did set the fan control signal (input 7) to -1 but, the outlet water temperature is still higher than the desired outlet temperature.For example,the desired outlet temperature was
 set at 24C as the 8th input, but the outlet fluid temperature was 29C. What is the reason for not achieving the desired outlet fluid temperature?<br>
</p>
<p><br>
</p>
<p>Regards<br>
</p>
<p>Idris<br>
</p>
<p><br>
</p>
<hr tabindex="-1" style="display:inline-block; width:98%">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" color="#000000" style="font-size:11pt"><b>From:</b> David BRADLEY <d.bradley@tess-inc.com><br>
<b>Sent:</b> 01 May 2015 17:04<br>
<b>To:</b> Shofolahan, Idris Adewale; TRNSYS users mailing list at OneBuilding.org<br>
<b>Subject:</b> Re: [TRNSYS-users] Type 510 cooling tower -Fan control signal error</font>
<div> </div>
</div>
<div>Idris,<br>
 The design outlet fluid temperature is the outlet fluid temperature that you would get if all the inlet conditions were at the design condition. The design outlet fluid temperature is not a "set point" temperature that the tower is trying to achieve. If you
 are trying to achieve a certain outlet temperature then you have to set that temperature as the 8th input and you have to set the fan control signal (input 7) to -1 (as it says in the "more" buttons for the Type). If you are not trying to control the outlet
 liquid temperature but just want it to be closer to the wetbulb temperature then you have to increase the air flow rate that the fans are providing.<br>
 regards,<br>
  David<br>
 <br>
<br>
<div class="moz-cite-prefix">On 4/30/2015 5:45 PM, Shofolahan, Idris Adewale wrote:<br>
</div>
<blockquote type="cite">
<div id="divtagdefaultwrapper" style="font-size:12pt; color:#000000; background-color:#FFFFFF; font-family:Calibri,Arial,Helvetica,sans-serif">
<p>David,<br>
</p>
<p><br>
</p>
<p>Thank you for your response.I have checked the parameters as suggested.The design outlet fluid temperature was not below the design wet bulb temperature. Although,when I reduce the design wet bulb temperature,I didn't get any error message.</p>
<p><br>
</p>
<p>However,the outlet water temperature is higher than the design outlet fluid temperature. How can I achieve a lower outlet water temperature,probably similar to the <span style="font-family:Calibri,Arial,Helvetica,sans-serif; font-size:16px; background-color:rgb(255,255,255)">design
 outlet </span><span style="font-family:Calibri,Arial,Helvetica,sans-serif; font-size:16px; background-color:rgb(255,255,255)">fluid temperature or lower?</span><br>
</p>
<p><br>
</p>
<div id="Signature">
<div name="divtagdefaultwrapper" style="font-family:Calibri,Arial,Helvetica,sans-serif; font-size:; margin:0">
<p>Regards,<br>
</p>
<p>Idris<br>
</p>
<p><br>
</p>
<p> </p>
<p> </p>
</div>
</div>
<div style="color:rgb(0,0,0)">
<hr tabindex="-1" style="display:inline-block; width:98%">
<div id="divRplyFwdMsg" dir="ltr"><font color="#000000" face="Calibri, sans-serif" style="font-size:11pt"><b>From:</b> David BRADLEY
<a class="moz-txt-link-rfc2396E" href="mailto:d.bradley@tess-inc.com"><d.bradley@tess-inc.com></a><br>
<b>Sent:</b> 30 April 2015 15:35<br>
<b>To:</b> TRNSYS users mailing list at OneBuilding.org; Shofolahan, Idris Adewale<br>
<b>Subject:</b> Re: [TRNSYS-users] Type 510 cooling tower -Fan control signal error</font>
<div> </div>
</div>
<div>Idris,<br>
  The error message doesn't have to do with the fan control signal. The error is that the model cannot determine the energy transfer coefficients for the tower given the parameters that you have entered. For example, if you give a design outlet fluid temperature
 that is below the design wet bulb temperature then it is physically impossible for a tower to deliver such an outlet water temperature and the model will generate the error that you received. The fan control signal appears involved because the energy transfer
 coefficients are only calculated if the tower is actually on and running.<br>
regards,<br>
 David<br>
 <br>
<br>
<div class="moz-cite-prefix">On 4/30/2015 12:20 AM, Shofolahan, Idris Adewale wrote:<br>
</div>
<blockquote type="cite">
<pre>Dear all,
I'm currently working on a project using a chiller and type 510 cooling tower. The project is given error when the fan control signal is set at 1 at the input tab. What do you think is the cause of this error? Schematics and error message of the project attached.Thank you.
Regards,
Idris
________________________________________
From: TRNSYS-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a> on behalf of <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a> <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-request@lists.onebuilding.org"><trnsys-users-request@lists.onebuilding.org></a>
Sent: 29 April 2015 21:08
To: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
Subject: TRNSYS-users Digest, Vol 124, Issue 42
Send TRNSYS-users mailing list submissions to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
To subscribe or unsubscribe via the World Wide Web, visit
        <a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
or, via email, send a message with subject or body 'help' to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a>
You can reach the person managing the list at
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Copyright in this email and in any attachments belongs to London South Bank University. This email, and its attachments if any, may be confidential or legally privileged and is intended to be seen only by the person to whom it is addressed. If you are not the intended recipient, please note the following: (1) You should take immediate action to notify the sender and delete the original email and all copies from your computer systems; (2) You should not read copy or use the contents of the email nor disclose it or its existence to anyone else. The views expressed herein are those of the author(s) and should not be taken as those of London South Bank University, unless this is specifically stated. London South Bank University is a company limited by guarantee registered in England and Wales. The following details apply to London South Bank University: Company number - 00986761; Registered office and trading address - 103 Borough Road London SE1 0AA; VAT number - 778 1116 17 Ema
 il addr
ess - <a class="moz-txt-link-abbreviated" href="mailto:LSBUinfo@lsbu.ac.uk">LSBUinfo@lsbu.ac.uk</a>
============================================
The LSBU communications disclaimer can be found at <a class="moz-txt-link-freetext" href="http://www.lsbu.ac.uk/ict/legal/">http://www.lsbu.ac.uk/ict/legal/</a>
</pre>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset> <br>
<pre>_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
Copyright in this email and in any attachments belongs to London South Bank University. This email, and its attachments if any, may be confidential or legally privileged and is intended to be seen only by the person to whom it is addressed. If you are not the
 intended recipient, please note the following: (1) You should take immediate action to notify the sender and delete the original email and all copies from your computer systems; (2) You should not read copy or use the contents of the email nor disclose it
 or its existence to anyone else. The views expressed herein are those of the author(s) and should not be taken as those of London South Bank University, unless this is specifically stated. London South Bank University is a company limited by guarantee registered
 in England and Wales. The following details apply to London South Bank University: Company number - 00986761; Registered office and trading address - 103 Borough Road London SE1 0AA; VAT number - 778 1116 17 Email address -
<a class="moz-txt-link-abbreviated" href="mailto:LSBUinfo@lsbu.ac.uk">LSBUinfo@lsbu.ac.uk</a>
</div>
</div>
</div>
============================================<br>
The LSBU communications disclaimer can be found at <a class="moz-txt-link-freetext" href="http://www.lsbu.ac.uk/ict/legal/">
http://www.lsbu.ac.uk/ict/legal/</a> </blockquote>
<br>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</div>
</div>
============================================<br>
The LSBU communications disclaimer can be found at http://www.lsbu.ac.uk/ict/legal/
</body>
</html>