    Idris,<br>
     The design outlet fluid temperature is the outlet fluid temperature
    that you would get if all the inlet conditions were at the design
    condition. The design outlet fluid temperature is not a "set point"
    temperature that the tower is trying to achieve. If you are trying
    to achieve a certain outlet temperature then you have to set that
    temperature as the 8th input and you have to set the fan control
    signal (input 7) to -1 (as it says in the "more" buttons for the
    Type). If you are not trying to control the outlet liquid
    temperature but just want it to be closer to the wetbulb temperature
    then you have to increase the air flow rate that the fans are
    providing.<br>
     regards,<br>
      David<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 4/30/2015 5:45 PM, Shofolahan, Idris
      Adewale wrote:<br>
    </div>
    <blockquote cite="mid:1430433902571.47620@lsbu.ac.uk" type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
      <div id="divtagdefaultwrapper"
style="font-size:12pt;color:#000000;background-color:#FFFFFF;font-family:Calibri,Arial,Helvetica,sans-serif;">
        <p>David,<br>
        </p>
        <p><br>
        </p>
        <p>Thank you for your response.I have checked the parameters as
          suggested.The design outlet fluid temperature was not below
          the design wet bulb temperature. Although,when I reduce the
          design wet bulb temperature,I didn't get any error message.</p>
        <p><br>
        </p>
        <p>However,the outlet water temperature is higher than the
          design outlet fluid temperature. How can I achieve a lower
          outlet water temperature,probably similar to the <span
            style="font-family: Calibri, Arial, Helvetica, sans-serif;
            font-size: 16px; background-color: rgb(255, 255, 255);">design
            outlet </span><span style="font-family: Calibri, Arial,
            Helvetica, sans-serif; font-size: 16px; background-color:
            rgb(255, 255, 255);">fluid temperature or lower?</span><br>
        </p>
        <p><br>
        </p>
        <div id="Signature">
          <div name="divtagdefaultwrapper"
            style="font-family:Calibri,Arial,Helvetica,sans-serif;
            font-size:; margin:0">
            <p>Regards,<br>
            </p>
            <p>Idris<br>
            </p>
            <p><br>
            </p>
            <p> </p>
            <p> </p>
          </div>
        </div>
        <div style="color: rgb(0, 0, 0);">
          <hr tabindex="-1" style="display:inline-block; width:98%">
          <div id="divRplyFwdMsg" dir="ltr"><font style="font-size:11pt"
              color="#000000" face="Calibri, sans-serif"><b>From:</b>
              David BRADLEY <a class="moz-txt-link-rfc2396E" href="mailto:d.bradley@tess-inc.com"><d.bradley@tess-inc.com></a><br>
              <b>Sent:</b> 30 April 2015 15:35<br>
              <b>To:</b> TRNSYS users mailing list at OneBuilding.org;
              Shofolahan, Idris Adewale<br>
              <b>Subject:</b> Re: [TRNSYS-users] Type 510 cooling tower
              -Fan control signal error</font>
            <div> </div>
          </div>
          <div>Idris,<br>
              The error message doesn't have to do with the fan control
            signal. The error is that the model cannot determine the
            energy transfer coefficients for the tower given the
            parameters that you have entered. For example, if you give a
            design outlet fluid temperature that is below the design wet
            bulb temperature then it is physically impossible for a
            tower to deliver such an outlet water temperature and the
            model will generate the error that you received. The fan
            control signal appears involved because the energy transfer
            coefficients are only calculated if the tower is actually on
            and running.<br>
            regards,<br>
             David<br>
             <br>
            <br>
            <div class="moz-cite-prefix">On 4/30/2015 12:20 AM,
              Shofolahan, Idris Adewale wrote:<br>
            </div>
            <blockquote type="cite">
              <pre>Dear all,
I'm currently working on a project using a chiller and type 510 cooling tower. The project is given error when the fan control signal is set at 1 at the input tab. What do you think is the cause of this error? Schematics and error message of the project attached.Thank you.
Regards,
Idris
________________________________________
From: TRNSYS-users <a moz-do-not-send="true" class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a> on behalf of <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a> <a moz-do-not-send="true" class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-request@lists.onebuilding.org"><trnsys-users-request@lists.onebuilding.org></a>
Sent: 29 April 2015 21:08
To: <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
Subject: TRNSYS-users Digest, Vol 124, Issue 42
Send TRNSYS-users mailing list submissions to
        <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
To subscribe or unsubscribe via the World Wide Web, visit
        <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
or, via email, send a message with subject or body 'help' to
        <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a>
You can reach the person managing the list at
        <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Copyright in this email and in any attachments belongs to London South Bank University. This email, and its attachments if any, may be confidential or legally privileged and is intended to be seen only by the person to whom it is addressed. If you are not the intended recipient, please note the following: (1) You should take immediate action to notify the sender and delete the original email and all copies from your computer systems; (2) You should not read copy or use the contents of the email nor disclose it or its existence to anyone else. The views expressed herein are those of the author(s) and should not be taken as those of London South Bank University, unless this is specifically stated. London South Bank University is a company limited by guarantee registered in England and Wales. The following details apply to London South Bank University: Company number - 00986761; Registered office and trading address - 103 Borough Road London SE1 0AA; VAT number - 778 1116 17 Email addr
ess - <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:LSBUinfo@lsbu.ac.uk">LSBUinfo@lsbu.ac.uk</a>
============================================
The LSBU communications disclaimer can be found at <a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.lsbu.ac.uk/ict/legal/">http://www.lsbu.ac.uk/ict/legal/</a>
</pre>
              <br>
              <fieldset class="mimeAttachmentHeader"></fieldset>
              <br>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
            </blockquote>
            <br>
            <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
            Copyright in this email and in any attachments belongs to
            London South Bank University. This email, and its
            attachments if any, may be confidential or legally
            privileged and is intended to be seen only by the person to
            whom it is addressed. If you are not the intended recipient,
            please note the following: (1) You should take immediate
            action to notify the sender and delete the original email
            and all copies from your computer systems; (2) You should
            not read copy or use the contents of the email nor disclose
            it or its existence to anyone else. The views expressed
            herein are those of the author(s) and should not be taken as
            those of London South Bank University, unless this is
            specifically stated. London South Bank University is a
            company limited by guarantee registered in England and
            Wales. The following details apply to London South Bank
            University: Company number - 00986761; Registered office and
            trading address - 103 Borough Road London SE1 0AA; VAT
            number - 778 1116 17 Email address - <a class="moz-txt-link-abbreviated" href="mailto:LSBUinfo@lsbu.ac.uk">LSBUinfo@lsbu.ac.uk</a>
          </div>
        </div>
      </div>
      ============================================<br>
      The LSBU communications disclaimer can be found at
      <a class="moz-txt-link-freetext" href="http://www.lsbu.ac.uk/ict/legal/">http://www.lsbu.ac.uk/ict/legal/</a>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>