    Marko,<br>
     The reason that the "airlayer" material in the TRNBuild libraries
    is massless and has no thickness is that narrow air gaps (i.e.
    airgaps with little or no convection in them) can be assumed to
    provide thermal resistance in the wall. When you have a wide air gap
    then the convection within that airgap becomes important and you
    cannot correctly account for it as though it were part of the wall.
    What I would recommend you do is to treat that 70cm air gap as
    though it were one or more airnodes separated from the ambient and
    the conditioned space by "walls" that consist only of your polyester
    foil (treated as massless layers offering only a thermal
    resistance). You can set the convection coefficients on the inside
    of those two layers as computed internally by Type56. This is
    probably still not an ideal treatment of the situation either but in
    my opinion it is more correct than lumping the air gap into the
    wall.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/29/2015 1:58 PM, Marko Mancic
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1120083704.359120.1430333883099.JavaMail.yahoo@mail.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff;
        font-family:HelveticaNeue, Helvetica Neue, Helvetica, Arial,
        Lucida Grande, sans-serif;font-size:16px">
        <div id="yui_3_16_0_1_1430325183282_59393"> Hi Trnsys users,</div>
        <div id="yui_3_16_0_1_1430325183282_59392"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59377" dir="ltr">I am trying
          to create a model of a lightweight contruction sport hall,
          which consists of two leyers of special Polyester foils, and a
          70cm air layer between. In reality, the construction is
          streched and held in place by a wood sceleton.</div>
        <div id="yui_3_16_0_1_1430325183282_59466"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59467" dir="ltr">I have
          noticed, that whichever air layer is chosen from the library,
          it is modelled as massless, and the tickness is 0. </div>
        <div id="yui_3_16_0_1_1430325183282_59469"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59484">How can I change the
          tickness of the Air layer?</div>
        <div id="yui_3_16_0_1_1430325183282_59451" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59434" dir="ltr">In
          addition, I get the following error messages when I try to
          save the project "error when trying to create wall transfer
          coefficients"</div>
        <div id="yui_3_16_0_1_1430325183282_59450">" unable to find
          root, after indication that root exists"</div>
        <div id="yui_3_16_0_1_1430325183282_59449">"Maybe time base is
          to small"</div>
        <div id="yui_3_16_0_1_1430325183282_59469"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59485">What could be the
          couse of the error I am getting?</div>
        <div id="yui_3_16_0_1_1430325183282_59486"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59494"><br>
        </div>
        <div id="yui_3_16_0_1_1430325183282_59495">Thank you for
          helping!</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>