    Idris,<br>
      The error message doesn't have to do with the fan control signal.
    The error is that the model cannot determine the energy transfer
    coefficients for the tower given the parameters that you have
    entered. For example, if you give a design outlet fluid temperature
    that is below the design wet bulb temperature then it is physically
    impossible for a tower to deliver such an outlet water temperature
    and the model will generate the error that you received. The fan
    control signal appears involved because the energy transfer
    coefficients are only calculated if the tower is actually on and
    running.<br>
    regards,<br>
     David<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 4/30/2015 12:20 AM, Shofolahan,
      Idris Adewale wrote:<br>
    </div>
    <blockquote cite="mid:1430371245435.18921@lsbu.ac.uk" type="cite">
      <pre wrap="">Dear all,

I'm currently working on a project using a chiller and type 510 cooling tower. The project is given error when the fan control signal is set at 1 at the input tab. What do you think is the cause of this error? Schematics and error message of the project attached.Thank you.

Regards,
Idris

________________________________________
From: TRNSYS-users <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a> on behalf of <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a> <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-request@lists.onebuilding.org"><trnsys-users-request@lists.onebuilding.org></a>
Sent: 29 April 2015 21:08
To: <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
Subject: TRNSYS-users Digest, Vol 124, Issue 42

Send TRNSYS-users mailing list submissions to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>

To subscribe or unsubscribe via the World Wide Web, visit
        <a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>

or, via email, send a message with subject or body 'help' to
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a>

You can reach the person managing the list at
        <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Copyright in this email and in any attachments belongs to London South Bank University. This email, and its attachments if any, may be confidential or legally privileged and is intended to be seen only by the person to whom it is addressed. If you are not the intended recipient, please note the following: (1) You should take immediate action to notify the sender and delete the original email and all copies from your computer systems; (2) You should not read copy or use the contents of the email nor disclose it or its existence to anyone else. The views expressed herein are those of the author(s) and should not be taken as those of London South Bank University, unless this is specifically stated. London South Bank University is a company limited by guarantee registered in England and Wales. The following details apply to London South Bank University: Company number - 00986761; Registered office and trading address - 103 Borough Road London SE1 0AA; VAT number - 778 1116 17 Email addr
ess - <a class="moz-txt-link-abbreviated" href="mailto:LSBUinfo@lsbu.ac.uk">LSBUinfo@lsbu.ac.uk</a>
============================================
The LSBU communications disclaimer can be found at <a class="moz-txt-link-freetext" href="http://www.lsbu.ac.uk/ict/legal/">http://www.lsbu.ac.uk/ict/legal/</a>
</pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>