    Anand,<br>
     Yes, you can split the living room floor into two floors. If you
    are constructing the building in Trnsys3D simply draw a line down
    the middle of the living room and you will end up with two floor
    surfaces in the zone when you look at it in TRNBuild. <br>
    <br>
     I might point out as a side note, however, that this kind of issue
    happens all the time in buildings with radiant floors and that the
    solution is to simply put additional radiant floor piping loops into
    the larger zones and to valve the hydronic system so that the
    radiant floor in the larger zone gets more water flow than the
    others when it is calling for heating. The only reason (in my mind)
    to split the active floor into two parts in TRNBuild is if you want
    to be able to control those parts separately (i.e. send water flow
    to one half of the living room but not to the other half).<br>
    regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/24/2015 4:11 AM, Anand Narasipuram
      wrote:<br>
    </div>
    <blockquote
cite="mid:1448529809.1717225.1429866673589.JavaMail.yahoo@mail.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff;
        font-family:HelveticaNeue, Helvetica Neue, Helvetica, Arial,
        Lucida Grande, sans-serif;font-size:16px">
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Hello TRNSYS
          users,</div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">    I am
          very new to TRNSYS. I have a question regarding the active
          layer implementation. </div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Question:
          The living room (zone) in an apartment is very big and the
          heat flow rate when calculated is double the flow rate than
          the other rooms. Will it be possible to divide one zone(living
          room) into two different zones for active layer
          implementation? If not what is the best alternative solution.?</div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Please let
          me know your views.</div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr"><br>
        </div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Thanks in
          advance,</div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Regards,</div>
        <div id="yui_3_16_0_1_1429866268903_2832" dir="ltr">Anand.</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>