    Manrique,<br>
      If you are modeling a tempering valve, then the control signal for
    the mixing valve is actually calculated at the diverter where the
    flow of liquid splits into the portion that will go to the heat
    source and the portion that will be used to temper the heat source
    if it gets too hot. Have a look at Type11b. You can then use a
    simple flow mixer (i.e. not a controlled one) in order to remix the
    two liquid streams. If your situation is different then you can
    always write an equation that takes the temperature of the two
    streams as inputs and computes the fraction of each that is needed
    in order to arrive at your desired temperature.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/21/2015 7:04 AM, Manrique Delgado
      Benjamin wrote:<br>
    </div>
    <blockquote
      cite="mid:F4C3FCA031947747A22107837C393563124D29@EXMDB05.org.aalto.fi"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 2.0cm 70.85pt 2.0cm;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-US">Hi,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I want to implement a
            flow mixer with a defined outlet temperature. The
            description of Type 11d seems to be what I need:<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">“This instance of the
            Type11 model uses mode 3 to model a controlled flow mixer in
            which two inlet liquid streams are mixed together according
            to an internally calculated control function so as to
            <b>maintain the mixed outlet temperature at or below a user
              specified value</b>.”<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">However, there isn’t any
            input where to specify the outlet temperature. Do I need to
            calculate separately the control signal? If so, then what is
            the advantage of using this type instead of a simple
            Tee-piece?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Thanks,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Benjamin Manrique<o:p></o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>