Safwan,<br>
There is a very important difference between a building cooling
load and the total heat transfer rate being computed by Type697. A
building total cooling load is the amount of energy (sensible and
latent) that must be removed from a space in order to maintain a
setpoint. Type697 is reporting the amount of energy that it actually
removed from the air stream. If Type697 isn't maintaining the
setpoints that you want it to then the amount of energy that it is
removing from the space and the building's cooling load are not
going to be equivalent. <br>
I would recommend that you go through the tutorial called
"Temperature Level Control from Energy Rate Control" that can be
downloaded from:
<a class="moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm</a>.
The tutorial should answer your questions about the how to obtain
the loads or the energy transferred by the system. <br>
regards,<br>
David<br>
<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 4/6/2015 9:41 PM, Safwan Kanan
wrote:<br>
</div>
<blockquote
cite="mid:1517046859.924223.1428374519368.JavaMail.yahoo@mail.yahoo.com"
type="cite">
<div style="color:#000; background-color:#fff;
font-family:HelveticaNeue-Light, Helvetica Neue Light, Helvetica
Neue, Helvetica, Arial, Lucida Grande,
sans-serif;font-size:13px">
<div dir="ltr" id="yui_3_16_0_1_1428373760624_5070">Dear All,</div>
<div id="yui_3_16_0_1_1428373760624_5245" dir="ltr"><br>
</div>
<div id="yui_3_16_0_1_1428373760624_5246" dir="ltr">I am
simulating solar cooling system, shall I depend on total heat
transfer rate output from Type 697( cooling coil) as a cooling
load for building or not? If not shall I need to calculate the
cooling load for building by Trnsys? if yes ,could you please
explain HOW in details? I used Type 56.</div>
<div id="yui_3_16_0_1_1428373760624_5355" dir="ltr"><br>
</div>
<div id="yui_3_16_0_1_1428373760624_5400" dir="ltr">I am looking
forward to hearing from you.<br>
</div>
<div id="yui_3_16_0_1_1428373760624_5384" dir="ltr">Regards,</div>
<div id="yui_3_16_0_1_1428373760624_5386" dir="ltr"><br>
</div>
<div id="yui_3_16_0_1_1428373760624_5401" dir="ltr">Safwan Kanan</div>
<div id="yui_3_16_0_1_1428373760624_5402" dir="ltr">The
University of Manchester</div>
<div id="yui_3_16_0_1_1428373760624_5403" dir="ltr">Manchester</div>
<div id="yui_3_16_0_1_1428373760624_5404" dir="ltr">M13 9PL</div>
<div id="yui_3_16_0_1_1428373760624_5407" dir="ltr">UK<br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>