    David,<br>
      Your methodology would certainly work so long as you are not using
    a shading mask (*.shm file) in Type56. If you are using the shading
    mask that TRNBuild can generate then make sure that your buildings
    are all drawn far away from each other in Trnsys3D so that they do
    not shade each other.<br>
      <br>
      When I have simulations in which I am dealing with many slight
    variations from one project to another I rely quite a lot on a
    text-compare tool such as CompareIt and I look a lot at the *.dck
    and *.b17 files. Even if you aren't very familiar with the syntax of
    these files the differences from one project to another become much
    more obvious than if you are looking at those same differences from
    the respective interfaces (Studio and TRNBuild). I still make all my
    changes in the interfaces and I use the comparison tool just to make
    sure that there aren't any unintentional differences between the
    projects.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/13/2015 7:46 AM, David Geiger
      wrote:<br>
    </div>
    <blockquote
cite="mid:trinity-92cf7caa-9195-4be7-90f4-3227e9daef53-1428929171719@3capp-webde-bs10"
      type="cite">
      <div style="font-family: Verdana;font-size: 12.0px;">
        <div>Dear all,</div>
        <div> </div>
        <div>I'm tasked with simulating different optimisation
          strategies for serveral buildings. There are about 10
          buildings with</div>
        <div>3-5 strategies mainly consisting of changing only wall
          layers or windows. My first approach was to create a base
          version</div>
        <div>and then copy the project file for each variant. But this
          leads to quite a few project files and makes adding or
          changing</div>
        <div>things like heating types or schedules tedious and prone to
          errors.</div>
        <div>An idea was to create just one building project file per
          building with several independent zones which contain the</div>
        <div>walls/windows of the different variants. Are there any
          drawbacks to this approach? Or does TRNBuild include a
          solution</div>
        <div>that I'm not aware of? And if not, how do/would you handle
          this?</div>
        <div> </div>
        <div>Thanks in advance!</div>
        <div> </div>
        <div>Regards,</div>
        <div>David</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>