    Donya,<br>
      Because the 3d model contains the geometry information needed to
    determine the solar radiation falling on each surface, Type56
    automatically gets solar radiation from the same data file as is
    being used to provide the ambient temperature. You should be able to
    use Type99 directly and Type56 should be able to pick up the
    radiation itself. If you want to be more transparent about it all
    (and provide the radiation yourself via individual links to the
    building model the way we used to do) then you can open the *.b17 in
    TRNBuild and double click on each of the orientations shown in the
    project info window. Set any of the orientations you want from
    "internal calculation" to "external by another component." When you
    return to the Studio and update the building variable list you will
    have three new inputs for each orientation in your building
    description.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/27/2015 7:38 AM, Donya Sheikh Khan
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAL6cxYnMnogc7Fg88jfYv+POco84Z-45KwWVDVJzV=uJ-94Obg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi,
        <div><br>
        </div>
        <div>When one generates a 3D model with the TRNSYS wizard, there
          is no connection made between the amount of radiation from
          type15 and TRNBuild type56. How does TRNBuild than receive
          information about the amount of radiation from the sun?</div>
        <div><br>
        </div>
        <div>The reason for asking is, that I would like to use my own
          weather data file (so I have to use type99 or similar), but if
          type56 doesn't need a link between weather file telling it the
          amount of radiation (from what I see), how can I use my own
          weather file?</div>
        <div>
          <div><br>
          </div>
          -- <br>
          <div class="gmail_signature">
            <div dir="ltr">
              <div>Regards</div>
              <div>Donya</div>
              <div><br>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>