    Farah,<br>
      You need to make sure that the version of the Type155.dll located
    in the ..\Trnsys17\Exe directory matches the version of MatLab that
    you are using. You should be able to find various versions of
    Type155.dll (compiled for different versions of Matlab) located in
    the ..\Trnsys17\Exe\DLLs\ directory.<br>
      Other common problems are 1. the path to Matlabs \bin directory
    appearing more than once in the environment variable path and 2. not
    having administrator control on the computer (both the user and the
    system need to have full control)<br>
    best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/12/2015 00:40, Farah KOJOK wrote:<br>
    </div>
    <blockquote
      cite="mid:DUB406-EAS428FB0E6E527E2AA4B95046D0060@phx.gbl"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=windows-1252">
      <div style="direction: ltr;">Dear Sir,</div>
      <div style="direction: ltr;">I try to run the simulation of Trnsys
        project calling Matlab.</div>
      <div style="direction: ltr;">I obtain a message error that the
        version of Matlab doesn't match with Trnsys requirement.</div>
      <div style="direction: ltr;">Note that 32-bit Matlab is installed
        on my computer using Windows 64-bit.</div>
      <div style="direction: ltr;">Best regards</div>
      <div style="direction: ltr;">Farah</div>
      <br>
      Sent from my iPhone
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>