Safwan,<br>
The Type917 example shows how a house can be cooled while heating
a tank of water. It isn't really appropriate to run the example in
the winter. In the climate used in the example, the house requires a
significant amount of heat. At first the water tank is cooled down
to provide heat to the house but the capacity of the heat pump is
such that it cannot provide as much heat as the house requires. The
house temperature falls and psychrometrics warnings begin to be
generated. Once the limit on warnings is reached the simulation
stops. The example is not intended to model a complete, realistic
system but to show how Type917 might be connected as part of a
system.<br>
<br>
If you intend to call Matlab as part of a TRNSYS simulation, you
can use Type155. You simply need to make sure that the version of
Type155.dll (located in the ..\Trnsys17\Exe directory matches your
version of Matlab). Type155 was developed to communicate with Matlab
releases 13, 14, and more recent. I am not sure whether it is
compatible with earlier releases. For additional information, please
refer to the Type155 section of the 04-MathematicalReference.pdf
manual.<br>
regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 2/10/2015 10:30, safone samsuddin
wrote:<br>
</div>
<blockquote
cite="mid:449513420.2028416.1423585820441.JavaMail.yahoo@mail.yahoo.com"
type="cite">
<div style="color:#000; background-color:#fff; font-family:times
new roman, new york, times, serif;font-size:12px">
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32005">Dear All, </div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32006"><br>
</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011">I was
trying to simulate the example for Type 917 Air to water heat
pump in the TRNSYS 17, however, the simulator couldn't run for
0- 744 hour as it gives error. Does anyone know how to solve
this?</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011"><br>
</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011">P/S: Does
anyone know how to connect Simulink Matlab R12 and TRNYS17?</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011"><br>
</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011">Thanks</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011"><br>
</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011">Regards</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011"><br>
</div>
<div dir="ltr" id="yui_3_16_0_1_1423581108352_32011">Safwan Sam</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>