    Avishek,<br>
      There are a number of issues with the project that you sent. <br>
    <br>
    First, the absorption chiller that you specified has a 425 ton
    capacity while the collector has a 2m2 area. There is no pump in the
    hot water loop to set the flow rate so because the absorption
    chiller appears first in the component order, the flow rate in that
    loop is a constant 58000 kg/h. There is no weather data reading
    component attached to the solar collector.<br>
    <br>
    Second, the cooling water loop components (tower and pump) do not
    appear to be sized to match the absorption chiller. The pump's rated
    capacity is 1000 kg/h while the default cooling water flow rate for
    the chiller is 279000 kg/h. There is no weather data reading
    component attached to the cooling tower.<br>
    <br>
    Third, I am not clear on the intent of the chilled water loop. The
    chilled water from the absorption chiller is passing across the
    source side of a liquid to liquid heat exchanger (which would cool
    down the liquid on the other side of the heat exchanger). However,
    the other side of the heat exchanger is connected to the air coming
    out of an electrically fired unit heater. Air presumably cooled down
    by the heat exchanger is then returned to the unit heater but the
    heater control signal is set so that the unit heater is not allowed
    to turn off.<br>
    <br>
    Thermally I would guess that since there is no heat input into the
    air circulating through the unit heater and the absorption chiller
    is set to be constantly on the air is being driven to absolute zero,
    well beyond the range of applicability for the psychrometrics
    routine.<br>
    <br>
    When working with TRNSYS simulations it is vitally important to
    construct systems one component at a time. The procedure that I
    follow is to select an appropriate model from the library then open
    it and make certain that its parameters are set appropriately for
    the size of equipment that I intend to model. It is also important
    to click on the "more" button for the parameters and for the input
    initial (and constant) values so that I understand what information
    they are asking me to provide. Once I have a component in place, I
    connect its inputs and then use an online plotter to watch whatever
    outputs are appropriate (usually temperatures and flow rates). I
    often make a guess as to what I think I should see at the output of
    a component, then run the simulation and test whether I was right or
    wrong. Once I understand the output then I add another component.
    Inputs that are not connected stay constant throughout your
    simulation. <br>
    <br>
    I would recommend that you start by specifying only the absorption
    chiller in your system and send the temperature and flow rate of its
    three liquid streams to an online plotter. Set the chiller's control
    signal using a forcing function so that it is on or off only as a
    function of time. Once you understand the behavior of the model then
    you could add a solar collector with a constant flow rate and a
    weather file. However, do not yet connect the hot water output of
    the chiller to the input of the solar collector. Connect only the
    outlet of the solar collector to the input of the absorption
    chiller. Set a constant flow rate into the collector by specifying
    an input flow rate but do not connect the input. Change the size of
    the solar collector until it is providing you with the temperature
    and flow rate of water that is required by the absorption chiller
    that you selected.<br>
    <br>
    Regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2/3/2015 06:42, avishek ray wrote:<br>
    </div>
    <blockquote
      cite="mid:1634524501.846800.1422967331700.JavaMail.yahoo@mail.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff;
        font-family:Helvetica Neue-Light, Helvetica Neue Light,
        Helvetica Neue, Helvetica, Arial, Lucida Grande,
        Sans-Serif;font-size:16px">
        <div id="yiv6181692330">
          <div id="yui_3_16_0_1_1422962920054_27579"
            style="color:#000;background-color:#fff;font-family:Helvetica
            Neue-Light, Helvetica Neue Light, Helvetica Neue, Helvetica,
            Arial, Lucida Grande, Sans-Serif;font-size:16px;">
            <div id="yiv6181692330">
              <div id="yiv6181692330yui_3_16_0_1_1422962920054_6439"
                style="color:#000;background-color:#fff;font-family:Helvetica
                Neue-Light, Helvetica Neue Light, Helvetica Neue,
                Helvetica, Arial, Lucida Grande,
                Sans-Serif;font-size:16px;">
                <div><span></span></div>
                <div id="yiv6181692330yui_3_16_0_1_1422962920054_3856">
                  <div id="yui_3_16_0_1_1422962920054_27617" dir="ltr"> Hi
                    All,</div>
                  <div id="yui_3_16_0_1_1422962920054_27791" dir="ltr">I
                    am a new user of TRNSYS. I have designed a solar hot
                    water fired vapour absorption cooling system of 1 TR
                    size. The diagram is given below. The error
                    displayed is having the message TRNSYS Message 114
                    ---- The utility routine PSYCHOMETRICS which
                    calculates the thermodynamic properties of moist air
                    has been calledwith wet bulb temparature above the
                    maximum wet bulb temparature for a given pressure.
                    please check the routine which calls the
                    PSYCHOMETRICS routine for possible sources of error.
                    The .tpf file is also attached. Please enlighten me
                    to overcome this error<br>
                  </div>
                </div>
                <div id="yiv6181692330yui_3_16_0_1_1422962920054_3857"
                  class="yiv6181692330signature">
                  <div id="yui_3_16_0_1_1422962920054_28188"><span
                      id="yui_3_16_0_1_1422962920054_27864"
                      style="font-style:italic;font-weight:bold;"><br>
                    </span></div>
                  <div id="yui_3_16_0_1_1422962920054_28382"><span
                      id="yui_3_16_0_1_1422962920054_27864"
                      style="font-style:italic;font-weight:bold;"><br>
                    </span></div>
                  <div id="yui_3_16_0_1_1422962920054_28384"><span
                      id="yui_3_16_0_1_1422962920054_27864"
                      style="font-style:italic;font-weight:bold;">Avishek
                      Ray</span></div>
                  <br>
                  <span
                    id="yiv6181692330yui_3_16_0_1_1422962920054_3858"
                    style="font-style:italic;">Research Fellow and
                    Teaching Assistant<br>
                    Department of Energy Management<br>
                    Indian Institute Of Social Welfare and Business
                    Management; Kolkata-700073</span><br>
                  <br>
                  <span
                    id="yiv6181692330yui_3_16_0_1_1422962920054_3859"
                    style="font-style:italic;">M:9038707191</span></div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>