<div>Thanks Marion!</div>
<div> </div>
<div>So there is a better option when not using Trnsys3d? It would be more important to get a detailed</div>
<div>zone-zone interaction than having the 3D radiation models.</div>
<div> </div>
<div>Cutting the hall in different zones would also be possible. Is there a limitation as to how the zones</div>
<div>might be shaped? For example L or H-shaped? Technically a shape like that would not create a hole,</div>
<div>but then the 3d-building documentation states that the zones "must be convex, meaning that every</div>
<div>surface in the zone should be in the line of sight with all other surfaces of the zone".</div>
<div>I suppose this also applies?</div>
<div> </div>
<div>
<div>Thanks again!</div>
<div>David</div>
<div> </div>
<div style="margin: 10.0px 5.0px 5.0px 10.0px;padding: 10.0px 0 10.0px 10.0px;border-left: 2.0px solid rgb(195,217,229);">
<div style="margin: 0 0 10.0px 0;"><b>Gesendet:</b> Mittwoch, 07. Januar 2015 um 11:13 Uhr<br/>
<b>Von:</b> "Marion Hiller" <Hiller@Transsolar.com><br/>
<b>An:</b> "'TRNSYS users mailing list at OneBuilding.org'" <trnsys-users@lists.onebuilding.org><br/>
<b>Betreff:</b> Re: [TRNSYS-users] How to best model zones in zones?</div>
<div>
<div>
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">David,</span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">A zone in Trnsys3d can’t have holes.</span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">In order to do so you need to compose the production hall into zone volumes that fulfil this requirement.</span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">Often halls are cut horizontal at upper machine level. </span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">Do you need 3D radiation modes?</span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);">Marion</span></p>
<div>
<p class="MsoNormal"><b><span style="font-size: 10.0pt;font-family: Arial , sans-serif;color: rgb(0,90,0);">-----------------------------------------------------------------------------------------------------------------------------------------------------------</span></b><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
<p class="MsoNormal"><b><span style="font-size: 10.0pt;font-family: Arial , sans-serif;color: rgb(0,90,0);">Dipl.-Ing. Marion Hiller </span></b><br/>
<b><span style="font-size: 10.0pt;font-family: Arial , sans-serif;color: rgb(0,112,0);">TRANSSOLAR Energietechnik GmbH </span></b><br/>
<b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(0,90,0);">Stuttgart - Munich - New York - Paris </span></b><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(0,112,0);"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(0,112,0);">t: <a><span style="color: rgb(0,112,0);">+49.711.67976.0</span></a> f: <a><span style="color: rgb(0,112,0);">+49.711.67976.11</span></a></span></b></p>
<p class="MsoNormal"><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(0,112,192);"><a href="http://www.transsolar.com/" target="_blank"><span style="color: rgb(0,112,192);">www.transsolar.com/</span></a></span></b><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(0,90,0);"> </span></b><br/>
<br/>
<b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(31,73,125);">KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden </span></b><br/>
<b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(31,73,125);">Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart </span></b></p>
<p class="MsoNormal"><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(31,73,125);">Amtsgericht Stuttgart - HRB 23347</span></b><b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(31,73,125);"> / Steuernummer: 99073/00911 / USt-IdNr.: DE 152272639</span></b><br/>
<b><span style="font-size: 7.5pt;font-family: Arial , sans-serif;color: rgb(31,73,125);">Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle </span></b></p>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
</div>
<p class="MsoNormal"><span style="font-size: 11.0pt;font-family: Calibri , sans-serif;color: rgb(31,73,125);"> </span></p>
<div>
<div style="border: none;border-top: solid rgb(181,196,223) 1.0pt;padding: 3.0pt 0.0cm 0.0cm 0.0cm;">
<p class="MsoNormal"><b><span style="font-size: 10.0pt;font-family: Tahoma , sans-serif;">Von:</span></b><span style="font-size: 10.0pt;font-family: Tahoma , sans-serif;"> TRNSYS-users [mailto:trnsys-users-bounces@lists.onebuilding.org] <b>Im Auftrag von </b>David Geiger<br/>
<b>Gesendet:</b> Mittwoch, 7. Januar 2015 10:33<br/>
<b>An:</b> trnsys-users@lists.onebuilding.org<br/>
<b>Betreff:</b> [TRNSYS-users] How to best model zones in zones?</span></p>
</div>
</div>
<p class="MsoNormal"> </p>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">Hello folks,</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">I'm trying to model a production hall containing enclosed machines. Since I am interested in the behavoir of the hall</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">as well as the machine enclosures, I was wondering if it is possible to define zones enclosed in other zones.</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">I tried this using the 3d-multizone builging but could only get the simulation to work when the boundary conditions of the machine</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">enclosures were set to "external". But I suppose that's like defining a shading group because the zones did not interact.</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">It feels like I'm missing a big point here, so any pointers are appreciated.</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">Thank you very much!</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">Kind regards,</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">David</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;"> </span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">___________________________</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">Dipl.-Wirtsch.-Ing David Geiger</span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size: 9.0pt;font-family: Verdana , sans-serif;">Universität Kassel</span></p>
</div>
</div>
</div>
</div>
_______________________________________________ TRNSYS-users mailing list TRNSYS-users@lists.onebuilding.org <a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></div>