      We have dealt with some similar cases where there is a large
    refrigerated box in the middle of a much larger zone. We simply
    define two zones with the walls of the refrigerated box enclosure
    being set as ADJACENT walls that separate the enclosure space from
    the larger zone volume. This means that you cannot do the detailed
    radiation exchange model in the larger zone (since it is no longer
    convex).<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 1/7/2015 03:32, David Geiger wrote:<br>
    </div>
    <blockquote
cite="mid:trinity-297c0f29-f42c-4121-afa9-0c463baffb40-1420623170812@3capp-webde-bs07"
      type="cite">
      <div style="font-family: Verdana;font-size: 12.0px;">
        <div>
          <div>Hello folks,</div>
          <div> </div>
          <div>I'm trying to model a production hall containing enclosed
            machines.  Since I am interested in the behavoir of the hall</div>
          <div>as well as the machine enclosures, I was wondering if it
            is possible to define zones enclosed in other zones.</div>
          <div>I tried this using the 3d-multizone builging but could
            only get the simulation to work when the boundary conditions
            of the machine</div>
          <div>enclosures were set to "external". But I suppose that's
            like defining a shading group because the zones did not
            interact.</div>
          <div>It feels like I'm missing a big point here, so any
            pointers are appreciated.</div>
          <div> </div>
          <div>Thank you very much!</div>
          <div> </div>
          <div>Kind regards,</div>
          <div>David</div>
          <div> </div>
          <div>___________________________</div>
          <div>Dipl.-Wirtsch.-Ing David Geiger</div>
          <div>Universität Kassel</div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>