    Giulia,<br>
      There are two things that you need to do. <br>
    <br>
    1. In TRNBuild, you need to go to the "project" window and double
    click on each of your ORIENTATIONS to make sure that each is set to
    "calculation of radiation data: external by another component" Once
    you have made the change, exit TRNBuild and when you are in the
    Studio, right click on the Type56 proforma and select "update
    building variable list." The Type56 INPUTs list should now include
    total radiation, beam radiation, and angle of incidence of beam
    radiation for each ORIENTATION in your building. <br>
    2. You need to use a Type16 in between your Type9 and your Type56 to
    take the raw solar radiation data from Type9 and compute the beam,
    total, and angle of incidence on all of the orientations in your
    building. I would recommend that you look carefully at the example
    located in:<br>
    <br>
    ..\Trnsys17\Examples\Reading Data Files\RadiationProcessing.tpf<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 12/22/2014 09:13, Giulia Zanardi
      wrote:<br>
    </div>
    <blockquote cite="mid:DUB126-W80CCACF67898D4FDF3ED15B5560@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr">Hello everyone, I'd like to ask something about how
        to import a different set of RADIATION data (.prn) and
        re-connect the new imported values to the building in the same
        way the file was originally and automatically created (after the
        importation of a .idf file from the Trnsys3d plugin for
        Sketchup) in TRNSYS 17.
        <div><br>
        </div>
        <div>I've already used this kind of procedure for temperature
          and relative humidity data, using a .prn input file and "Type
          9b", but this specific case seems a little bit different and
          difficult for me to understand. I also know that a specific
          Type should exist in order to automatically separate and
          re-distribute the new imported values to the corresponding
          facedes and so on..</div>
        <div><br>
        </div>
        <div>Any sort of advice would be really appreciated,</div>
        <div>Thank you,</div>
        <div>Giulia</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>