    Adam,<br>
      You should be in contact with your TRNSYS distributor to get the
    latest TESS Libraries release as it includes documentation for
    Type941. <br>
    <br>
      To answer your specific questions, yes, you do still have to
    provide a cooling data file to the model even if you're not going to
    use the heat pump in cooling mode. You don't need to worry about the
    contents of the file and can simply use the one that is provided by
    default.<br>
      <br>
      The data in both the heating and cooling performance files are
    normalized. Each performance value is divided by that same
    performance value at the heat pump's rated condition. The value at
    the rated condition is provided as a parameter to the model. For
    example, if the heat pump's rated heating capacity is 0.6kW and its
    heating capacity at current operating conditions is 0.8 kW then the
    normalized heating capacity value entered into the data file would
    be 0.8/0.6=1.333.<br>
    <br>
      As a final note, when heat pump performance data files are
    normalized they end up looking very similar to one another so
    chances are that you can use the data file that is provided as an
    example and be quite close to the actual performance of the heat
    pump that you are planning to use.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 12/17/2014 08:44, Adam O' Donovan
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAJU3Uzkb=pxJ+Jyxi_d4y1EjHSN4QPp=+zXgoT2es5jU18hyyg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi TRNSYS users,
        <div><br>
        </div>
        <div>I am currently modelling a heating system where the system
          is served by an air to water heat pump. I cannot seem to find
          the documentation on this and I was wondering if anyone knew
          what details need to be specified in the .dat file for heating
          and cooling. As the heat pump I have does not cool the DHW
          system what must I specify in the dat file. </div>
        <div><br>
        </div>
        <div>For the heating .dat file what is meant by "!Fraction
          capacity and power" what are the capacity and power divided by
          to give these fractions.</div>
        <div><br>
        </div>
        <div>Thank you,</div>
        <div><br>
        </div>
        <div>Adam.<br clear="all">
          <div><br>
          </div>
          -- <br>
          <div class="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div>
                    <div>Kind Regards,</div>
                    <div> </div>
                    <div>Adam Ó Donnabháin,</div>
                    <div>Postgraduate Researcher,</div>
                    <div>CIT,</div>
                    <div> </div>
                    <div> </div>
                    <div> </div>
                    <div><strong><font
                          style="background-color:rgb(0,153,0)">Please,
                          consider the environment before printing this
                          message.</font></strong></div>
                    <div> </div>
                    <div> </div>
                    <div> </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>