    Jorge,<br>
      The character combination *|( is recognized by TRNSED as the
    syntax for beginning a group of checkboxes. In the case of Type340 I
    guess that the proforma has a variable in it called (UA)s,a1.
    TRNEdit (which interprets TRNSED syntax) is getting confused by the
    open parenthesis character. It thinks a checkbox group is starting
    and doesn't understand that the "(" is part of the variable in a
    numerical value field.<br>
    <br>
      The way to fix the problem permanently is to edit the Type340
    proforma and change the name of the parameter so that it does not
    have a parenthesis as its first character, then right click on
    Type340 in your project and select "replace" from the context menu.
    Browse to find the location of the modified proforma and then
    generate your TRNSED application again.<br>
    <br>
      A much simpler fix would be to simply change the TRNSED line to
    read:<br>
    <br>
    <small><small><font face="Courier New, Courier, monospace">UASAHEAT=0
          <br>
          *|Heat loss capacity rate of the store through the first zone
          (dz1) of the store mantle
          |kJ/hr.K|kJ/hr.K|0|1|0|1000000.00000|1000
        </font></small></small><br>
    <br>
      With this second fix, the problem would come back if you were to
    ever generate another TRNSED application from a simulation that
    includes Type340.<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 12/9/2014 14:10, Jorge Facao wrote:<br>
    </div>
    <blockquote cite="mid:54875743.5020705@lneg.pt" type="cite">Dear
      TRNSYS users,
      <br>
      I am trying to make a TRNSED application.
      <br>
      My project includes the Type 340 - Multiport Store.
      <br>
      When I open the project.trd in TRNEDIT I receive an error message.
      <br>
      I made a simple project just with Type 340 and the message error
      is "Error in line 103. Checkbox command expected."
      <br>
      I copy the line 103 to this e-mail.
      <br>
      <br>
      UASAHEAT=0
      <br>
      *|(UA)s,a1
      <br>
      heat loss capacity rate of the store through the first zone (dz1)
      of the store mantle |kJ/hr.K|kJ/hr.K|0|1|0|1000000.00000|1000
      <br>
      <br>
      Looking forward to ear from you to solve this problem.
      <br>
      Best regards,
      <br>
      <br>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>