    Enyuan,<br>
    <br>
    1. That is correct.<br>
    <br>
    2. There is a lot of information in the data file. The file that you
    excerpted below is the heating performance data file and it says
    that the performance metrics are valid for return air temperatures
    (actually mixed return + outdoor air temperatures) between 15.6 and
    26.7C and for outdoor temperatures between -19.4 and 22.2C. If you
    look at the cooling performance data file you will find a line near
    the top of the file that has the comment "outdoor dry bulb" (or
    something like that). If you look at the minimum and maximum value
    on that line you will find the range of temperatures over which the
    cooling performance data is valid.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 11/21/2014 12:26, Enyuan Hu wrote:<br>
    </div>
    <blockquote
cite="mid:CAJud35MWueJV63Yn27Xh=3Bteq3JHQ_xfj8kXEW0_jibQV_ODw@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">Dear
          David,</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">As
          always, thank you so much for the informative answers. I'm
          trying to confirm if I understood correctly.</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">1.
          "...<span
            style="font-family:arial,sans-serif;font-size:13px;color:rgb(34,34,34)">It
            is computed as the mass flow rate of air multiplied by the
            difference between the enthalpy of air leaving the heat pump
            and the enthalpy of the mixed air (return + ambient)
            entering the evaporator"..."</span><span
            style="font-size:13px;font-family:arial,sans-serif;color:rgb(34,34,34)">It
            could be that your heat pump is cooling because there is no
            ambient air being mixed in and the heat pump is working only
            with return air...</span>" </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">so,
          as long as the enthalpy of entering air is larger than that of
          the leaving air, cooling rate will computed as positive,
          right? and this could happen even during the winter. One
          possibility is that there is no ambient air entering the heat
          pump and the entering air (only containing returned air) is
          even hotter than the leaving air, right?</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">2.
          "...<span
            style="font-family:arial,sans-serif;font-size:13px;color:rgb(34,34,34)">Performance
            is interpolated within the range of data given in the file
            but it is not extrapolated beyond the range...</span>"</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">I
          checked the external file and found something like:</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default" style="">
          <div class="gmail_default" style=""><font face="arial,
              helvetica, sans-serif" color="#3333ff">0.875<span class=""
                style="white-space:pre"> </span>1.000<span class=""
                style="white-space:pre"> </span>1.042<span class=""
                style="white-space:pre"> </span>!Normalized air flow
              rate<span class="" style="white-space:pre"> </span></font></div>
          <div class="gmail_default" style=""><font face="arial,
              helvetica, sans-serif" color="#3333ff">15.56<span class=""
                style="white-space:pre"> </span>21.11<span class=""
                style="white-space:pre"> </span>23.89<span class=""
                style="white-space:pre"> </span>26.67<span class=""
                style="white-space:pre"> </span>!Return air dry bulb
              temperature (C)<span class="" style="white-space:pre"> </span></font></div>
          <div class="gmail_default" style=""><font face="arial,
              helvetica, sans-serif" color="#3333ff">-19.44<span
                class="" style="white-space:pre"> </span>-16.67<span
                class="" style="white-space:pre"> </span>-13.89<span
                class="" style="white-space:pre"> </span>-11.11<span
                class="" style="white-space:pre"> </span>-8.33<span
                class="" style="white-space:pre"> </span>-5.56<span
                class="" style="white-space:pre"> </span>-2.78<span
                class="" style="white-space:pre"> </span>0<span
                class="" style="white-space:pre"> </span>2.78<span
                class="" style="white-space:pre"> </span>5.56<span
                class="" style="white-space:pre"> </span>8.33<span
                class="" style="white-space:pre"> </span>11.11<span
                class="" style="white-space:pre"> </span>13.89<span
                class="" style="white-space:pre"> </span>16.67<span
                class="" style="white-space:pre"> </span>19.44<span
                class="" style="white-space:pre"> </span>22.22<span
                class="" style="white-space:pre"> </span>!Outdoor dry
              bulb temperature (C)</font></div>
          <div class="gmail_default" style=""><font face="arial,
              helvetica, sans-serif" color="#3333ff">1.0000<span
                class="" style="white-space:pre"> </span>1.0000<span
                class="" style="white-space:pre"> </span></font></div>
          <div class="gmail_default" style=""><font face="arial,
              helvetica, sans-serif" color="#3333ff">1.1707<span
                class="" style="white-space:pre"> </span>1.0597<span
                class="" style="white-space:pre"> </span></font></div>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">...</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">I
          was wondering what kind of information we can learn from this
          file, especially in terms of the temperature range that gives
          valid computation like what you mentioned? Thanks!</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)"><br>
        </div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">best
          regards,</div>
        <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:rgb(51,51,255)">Enyuan</div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Thu, Nov 20, 2014 at 12:59 PM, <span
            dir="ltr"><<a moz-do-not-send="true"
              href="mailto:trnsys-users-request@lists.onebuilding.org"
              target="_blank">trnsys-users-request@lists.onebuilding.org</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
            TRNSYS-users mailing list submissions to<br>
                    <a moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br>
            <br>
            To subscribe or unsubscribe via the World Wide Web, visit<br>
                    <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
            <br>
            or, via email, send a message with subject or body 'help' to<br>
                    <a moz-do-not-send="true"
              href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a><br>
            <br>
            You can reach the person managing the list at<br>
                    <a moz-do-not-send="true"
              href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a><br>
            <br>
            When replying, please edit your Subject line so it is more
            specific<br>
            than "Re: Contents of TRNSYS-users digest..."<br>
            <br>
            Today's Topics:<br>
            <br>
               1. Re: total heating rate and total cooling rate in heat
            pump<br>
                  954 (David BRADLEY)<br>
               2. Re: (no subject) (haydar =?UTF-8?Q?kepek=C3=A7i?=)<br>
               3. Re: (no subject) (<a moz-do-not-send="true"
              href="mailto:mcdowell@tess-inc.com">mcdowell@tess-inc.com</a>)<br>
               4. Re: (no subject) (Jason Glazer)<br>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: David BRADLEY <<a moz-do-not-send="true"
              href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
            To: "TRNSYS users mailing list at OneBuilding.org" <<a
              moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>,
            trnsys-users <<a moz-do-not-send="true"
              href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
            Cc: <br>
            Date: Thu, 20 Nov 2014 09:59:49 -0600<br>
            Subject: Re: [TRNSYS-users] total heating rate and total
            cooling rate in heat pump 954<br>
            <div text="#000000" bgcolor="#FFFFFF"> Enyuan,<br>
                The total cooling rate is the sensible and latent energy
              being removed from the air stream by the active section of
              the heat pump. It is computed as the mass flow rate of air
              multiplied by the difference between the enthalpy of air
              leaving the heat pump and the enthalpy of the mixed air
              (return + ambient) entering the evaporator. The heat pump
              does not have any kind of economizer controls built into
              it. The amount of outdoor air being mixed with return air
              is simply a function of how you have set the outdoor air
              damper position input. It could be that your heat pump is
              cooling because there is no ambient air being mixed in and
              the heat pump is working only with return air. If your
              concern is that the heat pump would not operate when the
              ambient temperature is so low (because of freeze up in the
              condenser) then you have to be careful of your external
              data file. Performance is interpolated within the range of
              data given in the file but it is not extrapolated beyond
              the range. If the heat pump asks for cooling (because of
              the way you have set the cooling signal input and fan
              control signal) then the performance (cooling capacity and
              COP) will be returned for the closest ambient temperature
              found in the data file.<br>
              Regards,<br>
               David<br>
              <br>
              <br>
              <div>On 11/19/2014 14:26, Enyuan Hu wrote:<br>
              </div>
              <blockquote type="cite">
                <div dir="ltr">
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff">Dear

                    all,</div>
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff"><br>
                  </div>
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff">When

                    I'm using a type 954 air-to-air heat pump to
                    condition a one zone building, I found that even
                    during the winter (ambient temperature is below the
                    cooling threshold), the 'total cooling rate' output
                    from the heat pump is positive instead of being zero
                    as expected. Can anyone help me explain why? Thanks!</div>
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff"><br>
                  </div>
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff">best

                    regards,</div>
                  <div class="gmail_default"
style="font-family:arial,helvetica,sans-serif;font-size:small;color:#3333ff">Enyuan

                    Hu</div>
                </div>
                <br>
                <fieldset></fieldset>
                <br>
                <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
              </blockquote>
              <br>
              <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a moz-do-not-send="true" href="tel:%2B1.608.274.2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a moz-do-not-send="true" href="tel:%2B1.608.278.1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a moz-do-not-send="true" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
            </div>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: "haydar kepekçi" <<a moz-do-not-send="true"
              href="mailto:haydar389@gmail.com">haydar389@gmail.com</a>><br>
            To: "TRNSYS users mailing list at OneBuilding.org" <<a
              moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br>
            Cc: <br>
            Date: Thu, 20 Nov 2014 17:23:16 +0200<br>
            Subject: Re: [TRNSYS-users] (no subject)<br>
            <p dir="ltr">Dont send me e- mail !! I dont want to see ur
              words about Fucking trnsys !!!<br>
            </p>
            <p dir="ltr">Sent using <a moz-do-not-send="true"
href="https://cloudmagic.com/k/d/mailapp?ct=pa&cv=5.1.6.5&pv=4.3"
                target="_blank">CloudMagic</a></p>
            <br>
            <div style="color:#787878">On Per, Kas 20, 2014 at 4:32 PM,
              Ben Heymer <<a moz-do-not-send="true"
                href="mailto:bheymer@gmail.com" target="_blank">bheymer@gmail.com</a>>
              wrote:</div>
            <br>
            <div
              style="background-image:initial;background-color:rgb(255,255,255);background-repeat:initial
              initial">
              <blockquote>
                <p dir="ltr">You should look through your "Result" file
                  for the source of the error.
                  <br>
                  <br>
                  A common cause of errors of this type is convergence.
                  Make sure you
                  <br>
                  have enough volume in your water loop for at least 1
                  timestep of water
                  <br>
                  flow. Sometimes it's also helpful to connect the mass
                  flow output of
                  <br>
                  the pump right back to the mass flow input.
                  <br>
                  <br>
                  As a last resort, you can relax the convergence
                  parameters and error
                  <br>
                  thresholds in the control cards.
                  <br>
                  <br>
                  Ben Heymer, PE
                  <br>
                  <br>
                  On Thu, Nov 20, 2014 at 3:52 AM, Michael Stochniol
                  <br>
                  <<a moz-do-not-send="true"
                    href="mailto:stochnio@mail.hs-ulm.de"
                    target="_blank">stochnio@mail.hs-ulm.de</a>>
                  wrote:
                  <br>
                  > Hallo everyone,
                  <br>
                  >
                  <br>
                  > im trying to create a control function using
                  equations with logic operators for the control of a
                  variable speed pump, in order to adjust the massflow
                  trough the pump. I wrote a control funktion and
                  plotted it without connecting it to the pump and it
                  seemed to work right. But if i am conecting it to the
                  pump my simulation freezes after around 700 timesteps
                  or less. I am trying to create solar domestic hot
                  water system. The question is, is it possible to
                  create this kind of control circuit with equations ? I
                  have similar problems with every control loop i am
                  trying to create this way. The math should work but
                  implemented  in TRNSYS (TRNSYS 17) the simulation
                  stick somewhere.
                  <br>
                  >
                  <br>
                  > I am no experienced user so maybe someone could
                  give my some advise how to implement this kind of
                  control functions right?
                  <br>
                  >
                  <br>
                  > i am very grateful for any help or ideas.
                  <br>
                  >
                  <br>
                  > thanks in advance
                  <br>
                  >
                  <br>
                  > Michael Stochniol
                  <br>
                  > _______________________________________________
                  <br>
                  > TRNSYS-users mailing list
                  <br>
                  > <a moz-do-not-send="true"
                    href="mailto:TRNSYS-users@lists.onebuilding.org"
                    target="_blank">TRNSYS-users@lists.onebuilding.org</a>
                  <br>
                  > <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                    target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
                  <br>
                  _______________________________________________
                  <br>
                  TRNSYS-users mailing list
                  <br>
                  <a moz-do-not-send="true"
                    href="mailto:TRNSYS-users@lists.onebuilding.org"
                    target="_blank">TRNSYS-users@lists.onebuilding.org</a>
                  <br>
                  <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                    target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
                  <br>
                </p>
              </blockquote>
            </div>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: <a moz-do-not-send="true"
              href="mailto:mcdowell@tess-inc.com">mcdowell@tess-inc.com</a><br>
            To: "TRNSYS users mailing list at OneBuilding.org" <<a
              moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br>
            Cc: <br>
            Date: Thu, 20 Nov 2014 11:57:52 -0600<br>
            Subject: Re: [TRNSYS-users] (no subject)<br>
            <div>
              <p>Haydar Kepekci -</p>
              <p>Please use the links at the bottom of the email to
                unsubscribe from the TRNSYS mailing list. </p>
              <p>And please avoid using offensive language in email
                messages.</p>
              <p>Regards,</p>
              <p>Tim</p>
              <p> </p>
              <div>
                <pre>---
Timothy P. McDowell
Executive Vice President
Thermal Energy System Specialists, LLC
22 N Carroll St, Suite 370
Madison, WI 53703
<a moz-do-not-send="true" href="tel:608-274-2577" value="+16082742577" target="_blank">608-274-2577</a></pre>
              </div>
              <p>On 2014-11-20 09:23, haydar kepekçi wrote:</p>
              <blockquote type="cite"
                style="padding-left:5px;border-left:#1010ff 2px
                solid;margin-left:5px">
                <p dir="ltr">Dont send me e- mail !! I dont want to see
                  ur words about Fucking trnsys !!!</p>
                <p dir="ltr">Sent using <a moz-do-not-send="true"
href="https://cloudmagic.com/k/d/mailapp?ct=pa&cv=5.1.6.5&pv=4.3"
                    target="_blank">CloudMagic</a></p>
                <br>
                <div style="color:#787878">On Per, Kas 20, 2014 at 4:32
                  PM, Ben Heymer <<a moz-do-not-send="true"
                    href="mailto:bheymer@gmail.com" target="_blank">bheymer@gmail.com</a>>
                  wrote:</div>
                <br>
                <div
                  style="background-image:initial;background-color:#ffffff;background-repeat:initial
                  initial">
                  <blockquote type="cite"
                    style="padding-left:5px;border-left:#1010ff 2px
                    solid;margin-left:5px">
                    <p dir="ltr">You should look through your "Result"
                      file for the source of the error. <br>
                      <br>
                      A common cause of errors of this type is
                      convergence. Make sure you <br>
                      have enough volume in your water loop for at least
                      1 timestep of water <br>
                      flow. Sometimes it's also helpful to connect the
                      mass flow output of <br>
                      the pump right back to the mass flow input. <br>
                      <br>
                      As a last resort, you can relax the convergence
                      parameters and error <br>
                      thresholds in the control cards. <br>
                      <br>
                      Ben Heymer, PE <br>
                      <br>
                      On Thu, Nov 20, 2014 at 3:52 AM, Michael Stochniol
                      <br>
                      <<a moz-do-not-send="true"
                        href="mailto:stochnio@mail.hs-ulm.de"
                        target="_blank">stochnio@mail.hs-ulm.de</a>>
                      wrote: <br>
                      > Hallo everyone, <br>
                      > <br>
                      > im trying to create a control function using
                      equations with logic operators for the control of
                      a variable speed pump, in order to adjust the
                      massflow trough the pump. I wrote a control
                      funktion and plotted it without connecting it to
                      the pump and it seemed to work right. But if i am
                      conecting it to the pump my simulation freezes
                      after around 700 timesteps or less. I am trying to
                      create solar domestic hot water system. The
                      question is, is it possible to create this kind of
                      control circuit with equations ? I have similar
                      problems with every control loop i am trying to
                      create this way. The math should work but
                      implemented  in TRNSYS (TRNSYS 17) the simulation
                      stick somewhere. <br>
                      > <br>
                      > I am no experienced user so maybe someone
                      could give my some advise how to implement this
                      kind of control functions right? <br>
                      > <br>
                      > i am very grateful for any help or ideas. <br>
                      > <br>
                      > thanks in advance <br>
                      > <br>
                      > Michael Stochniol <br>
                      >
                      _______________________________________________ <br>
                      > TRNSYS-users mailing list <br>
                      > <a moz-do-not-send="true"
                        href="mailto:TRNSYS-users@lists.onebuilding.org"
                        target="_blank">TRNSYS-users@lists.onebuilding.org</a>
                      <br>
                      > <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                        target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
                      <br>
                      _______________________________________________ <br>
                      TRNSYS-users mailing list <br>
                      <a moz-do-not-send="true"
                        href="mailto:TRNSYS-users@lists.onebuilding.org"
                        target="_blank">TRNSYS-users@lists.onebuilding.org</a>
                      <br>
                      <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                        target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
                    </p>
                  </blockquote>
                </div>
                <br>
                <pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
              </blockquote>
            </div>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: Jason Glazer <<a moz-do-not-send="true"
              href="mailto:jglazer@gard.com">jglazer@gard.com</a>><br>
            To: <a moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br>
            Cc: <br>
            Date: Thu, 20 Nov 2014 11:59:19 -0600<br>
            Subject: Re: [TRNSYS-users] (no subject)<br>
            As a reminder, to unsubscribe just send a blank email to:<br>
            <br>
            <a moz-do-not-send="true"
              href="mailto:trnsys-users-unsubscribe@onebuilding.org"
              target="_blank">trnsys-users-unsubscribe@onebuilding.org</a><br>
            <br>
            Jason<br>
            <br>
            On 11/20/2014 9:23 AM, haydar kepekçi wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              Dont send me e- mail !! I dont want to see ur words about<br>
               trnsys !!!<br>
              <br>
              Sent using CloudMagic<br>
              <<a moz-do-not-send="true"
href="https://cloudmagic.com/k/d/mailapp?ct=pa&cv=5.1.6.5&pv=4.3"
                target="_blank">https://cloudmagic.com/k/d/mailapp?ct=pa&cv=5.1.6.5&pv=4.3</a>><br>
              <br>
              <br>
              On Per, Kas 20, 2014 at 4:32 PM, Ben Heymer<br>
              <<a moz-do-not-send="true"
                href="mailto:bheymer@gmail.com" target="_blank">bheymer@gmail.com</a>
              <mailto:<a moz-do-not-send="true"
                href="mailto:bheymer@gmail.com" target="_blank">bheymer@gmail.com</a>>>
              wrote:<br>
              <br>
                  You should look through your "Result" file for the<br>
                  source of the error.<br>
              <br>
                  A common cause of errors of this type is convergence.<br>
                  Make sure you<br>
                  have enough volume in your water loop for at least 1<br>
                  timestep of water<br>
                  flow. Sometimes it's also helpful to connect the mass<br>
                  flow output of<br>
                  the pump right back to the mass flow input.<br>
              <br>
                  As a last resort, you can relax the convergence<br>
                  parameters and error<br>
                  thresholds in the control cards.<br>
              <br>
                  Ben Heymer, PE<br>
              <br>
                  On Thu, Nov 20, 2014 at 3:52 AM, Michael Stochniol<br>
                  <<a moz-do-not-send="true"
                href="mailto:stochnio@mail.hs-ulm.de" target="_blank">stochnio@mail.hs-ulm.de</a>>
              wrote:<br>
                   > Hallo everyone,<br>
                   ><br>
                   > im trying to create a control function using<br>
                  equations with logic operators for the control of a<br>
                  variable speed pump, in order to adjust the massflow<br>
                  trough the pump. I wrote a control funktion and
              plotted<br>
                  it without connecting it to the pump and it seemed to<br>
                  work right. But if i am conecting it to the pump my<br>
                  simulation freezes after around 700 timesteps or less.
              I<br>
                  am trying to create solar domestic hot water system.
              The<br>
                  question is, is it possible to create this kind of<br>
                  control circuit with equations ? I have similar
              problems<br>
                  with every control loop i am trying to create this
              way.<br>
                  The math should work but implemented  in TRNSYS
              (TRNSYS<br>
                  17) the simulation stick somewhere.<br>
                   ><br>
                   > I am no experienced user so maybe someone could
              give<br>
                  my some advise how to implement this kind of control<br>
                  functions right?<br>
                   ><br>
                   > i am very grateful for any help or ideas.<br>
                   ><br>
                   > thanks in advance<br>
                   ><br>
                   > Michael Stochniol<br>
                   > _______________________________________________<br>
                   > TRNSYS-users mailing list<br>
                   > <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@lists.onebuilding.org"
                target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
                   ><br>
                  <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
              <br>
                  _______________________________________________<br>
                  TRNSYS-users mailing list<br>
                  <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@lists.onebuilding.org"
                target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
                  <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
              <br>
              <br>
              <br>
              <br>
              _______________________________________________<br>
              TRNSYS-users mailing list<br>
              <a moz-do-not-send="true"
                href="mailto:TRNSYS-users@lists.onebuilding.org"
                target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
              <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
              <br>
            </blockquote>
            <br>
            -- <br>
            Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair<br>
            Admin for <a moz-do-not-send="true"
              href="http://onebuilding.org" target="_blank">onebuilding.org</a>
            building performance mailing lists<br>
            <br>
            <br>
            _______________________________________________<br>
            TRNSYS-users mailing list<br>
            <a moz-do-not-send="true"
              href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br>
            <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>