<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Daniel,<br>
     I don't think that modifying the tolerances is going to help; it
    will more likely lead to convergence problems. You could consider
    increasing the timestep. The PV models are all quasi steady state
    models and so don't have any capacitance effects in them. Unless you
    are doing some fancy controls that require a short tiemstep, you
    could consider making it longer. <br>
     <br>
     I suspect that almost all of the simulation time is in the
    communication back and forth between Excel and TRNSYS. If you look
    at the *.lst file produced when the simulation runs you should find
    a breakdown of how much time was spent in each components.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/15/2014 02:57, Daniel Tallos
      wrote:<br>
    </div>
    <blockquote cite="mid:1410767847406.90613@anu.edu.au" type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <style type="text/css" style="display:none"><!-- p { margin-top: 0px; margin-bottom: 0px; }--></style>
      <p>Hi,<br>
      </p>
      <p><br>
      </p>
      <p>I have two projects running, both simulations for 25 years of
        PV-battery systems. The first contains an Excel input type which
        acts as a discharge controller, and the second is identical but
        without the Excel type. It takes approximately 2-5 minutes to
        run the non-Excel type project simulation for 25 years. So far I
        have calculated that the 25 year simulation including the Excel
        model will take 2 hours......... <br>
      </p>
      <p><br>
      </p>
      <p>Is there any advice for speeding up this simulation time (i.e.
        can I change the tolerances? etc.) because I don't think this
        will be good enough for the amount of runs I will be running.<br>
      </p>
      <p><br>
      </p>
      <p>Thanks.<br>
      </p>
      <p><br>
      </p>
      <p>Daniel.<br>
      </p>
      <p><br>
      </p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>