    Eleonora,<br>
     Your Type56 building is in Energy Rate Control meaning that you are
    predefining a zone temperature and allowing the model to compute the
    energy required to maintain that temperature (the load). When you
    want to simulate a system, you need to move from Energy Rate Control
    to Temperature Level Control where you allow the zone temperature to
    float, you define a thermostat and the equipment that will deliver
    energy to the space (a fan coil or a radiator). The thermostat will
    watch the zone temperature and turn on and off the equipment in an
    attempt to maintain the desired set point. There is a tutorial
    called "Temperature Level Control from Energy Rate Control"
    available at:<br>
    <br>
<a class="moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm</a><br>
    <br>
    It will step you through the process that you can then apply to your
    building and system.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/3/2014 13:13, ELEONORA SANESI
      wrote:<br>
    </div>
    <blockquote
cite="mid:CACp0Bc7-pup5oDvGwt3H=1j5oN+9sfQLsaBwaALe30R161WMqg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi I'm Eleonora and I study environmental
        engineering.
        <div>For my thesis next month I have to model a real simply
          building but I have a problem. </div>
        <div>My building have the solar thermal collectors link to the
          boiler link to a pump.</div>
        <div>My problems is how to link this sistem to my type56.</div>
        <div>I send you my project in the hope of your answer.</div>
        <div>Thanks a lot</div>
        <div>Eleonora Sanesi</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>