Eleonora,<br>
Your Type56 building is in Energy Rate Control meaning that you are
predefining a zone temperature and allowing the model to compute the
energy required to maintain that temperature (the load). When you
want to simulate a system, you need to move from Energy Rate Control
to Temperature Level Control where you allow the zone temperature to
float, you define a thermostat and the equipment that will deliver
energy to the space (a fan coil or a radiator). The thermostat will
watch the zone temperature and turn on and off the equipment in an
attempt to maintain the desired set point. There is a tutorial
called "Temperature Level Control from Energy Rate Control"
available at:<br>
<br>
<a class="moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm</a><br>
<br>
It will step you through the process that you can then apply to your
building and system.<br>
Regards,<br>
David<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 9/3/2014 13:13, ELEONORA SANESI
wrote:<br>
</div>
<blockquote
cite="mid:CACp0Bc7-pup5oDvGwt3H=1j5oN+9sfQLsaBwaALe30R161WMqg@mail.gmail.com"
type="cite">
<div dir="ltr">Hi I'm Eleonora and I study environmental
engineering.
<div>For my thesis next month I have to model a real simply
building but I have a problem. </div>
<div>My building have the solar thermal collectors link to the
boiler link to a pump.</div>
<div>My problems is how to link this sistem to my type56.</div>
<div>I send you my project in the hope of your answer.</div>
<div>Thanks a lot</div>
<div>Eleonora Sanesi</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>