    Shahen,<br>
      It is quite normal to get COPs higher than the rated one. The
    rated COP is simply the COP at a particular set of inlet conditions.
    Those inlet conditions are not necessarily the inlet conditions at
    which the machine operates at its most efficient point.<br>
    regards<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/3/2014 14:54, Shahen Fakhraldin
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1409774053.83482.YahooMailNeo@web121205.mail.ne1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff;
        font-family:verdana, helvetica, sans-serif;font-size:10pt">
        <div id="yiv6206190985">
          <div>
            <div style="color: rgb(0, 0, 0); font-family: verdana,
              helvetica, sans-serif; font-size: 10pt; background-color:
              rgb(255, 255, 255);">
              <div id="yiv6206190985">
                <div id="yiv6206190985yui_3_16_0_1_1409773050248_3885">
                  <div style="color: rgb(0, 0, 0); font-family: verdana,
                    helvetica, sans-serif; font-size: 10pt;
                    background-color: rgb(255, 255, 255);"
                    class="yiv6206190985yui_3_16_0_1_1409773050248_3785"
                    id="yiv6206190985yui_3_16_0_1_1409773050248_3884">
                    <div id="yiv6206190985">
                      <div
                        id="yiv6206190985yui_3_16_0_1_1409745842588_13618">
                        <div style="color: rgb(0, 0, 0); font-family:
                          verdana, helvetica, sans-serif; font-size:
                          10pt; background-color: rgb(255, 255, 255);"
                          class="yiv6206190985yui_3_16_0_1_1409745842588_13555
                          yiv6206190985yui_3_16_0_1_1409773050248_3786"
id="yiv6206190985yui_3_16_0_1_1409745842588_13617">
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            class="yiv6206190985" style=""><span
                              id="yiv6206190985yui_3_16_0_6_1409745842588_20"
                              class="yiv6206190985" style="">Dear TRNSYS
                              user,</span></div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13558
yiv6206190985yui_3_16_0_1_1409773050248_3789"><span
                              id="yiv6206190985yui_3_16_0_6_1409745842588_48"
                              class="yiv6206190985" style=""><br
                                style="">
                            </span></div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13561
yiv6206190985yui_3_16_0_1_1409773050248_3792">Did anyone face a problem
                            of getting COPs greater than the rated one
                            in a solar assisted absorption system? Where
                            COP rises to around (0.8) at the start of
                            the simulation and gets down to an average
                            (0.75) for the rest of the day, whilst the
                            rated cop is (0.7).</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color:rgb(0, 0,
                            0);font-size:13.63636302948px;font-family:verdana,
                            helvetica,
                            sans-serif;font-style:normal;background-color:transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13561
                            yiv6206190985yui_3_16_0_1_1409773050248_3792
                            yui_3_16_0_1_1409773050248_9826">I assumed
                            the set point temp for the Aux heater 70 C
                            and the <span
                              id="yiv62061909853459d9b6-39d5-4054-bab9-6e798f76eee5"
                              class="yiv6206190985GINGER_SOFTWARE_mark"><span
id="dec4abe9-44e7-4637-97da-6f7cc688bf54"
                                ginger_software_uiphraseguid="2ce9a1e6-59d4-4e10-9682-4aa25a79d428"
                                class="GINGER_SOFTWARE_mark">timestep</span></span> was
                            1min</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13562
yiv6206190985yui_3_16_0_1_1409773050248_3793"><br
                              id="yiv6206190985yui_3_16_0_6_1409745842588_328"
                              class="yiv6206190985" style="">
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13564
yiv6206190985yui_3_16_0_1_1409773050248_3795">In my project, a cold tank
                            (type 4) is used to connect between the
                            chiller and the building, with the aid of
                            using type 682 to impose the load.</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13565
yiv6206190985yui_3_16_0_1_1409773050248_3796"><span
                              style="font-size:13.63636302948px;background-color:transparent;"
id="yiv6206190985yui_3_16_0_6_1409773050248_24">Is it resulted from a
                              mistake in the connections of the cold
                              tank? </span><br>
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13568
yiv6206190985yui_3_16_0_1_1409773050248_3799"><br>
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13568
yiv6206190985yui_3_16_0_1_1409773050248_3799">Down below are the <span
style="font-size:13.63636302948px;background-color:transparent;"
                              id="yiv6206190985yui_3_16_0_1_1409745842588_6206"
                              class="yiv6206190985">links</span><span
                              style="font-size:13.63636302948px;background-color:transparent;"
id="yiv6206190985yui_3_16_0_1_1409745842588_6206" class="yiv6206190985">, where
                              a&b for chiller-tank loop and c&d
                              for tank-load loop</span></div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_4"
                            style="color: rgb(0, 0, 0); font-size:
                            13.63636302948px; font-family: verdana,
                            helvetica, sans-serif; font-style: normal;
                            background-color: transparent;"
                            class="yiv6206190985
                            yiv6206190985yui_3_16_0_1_1409745842588_13568
yiv6206190985yui_3_16_0_1_1409773050248_3802"><span
                              class="yiv6206190985"
                              id="yiv6206190985yui_3_16_0_6_1409745842588_164"
style="font-size:13.63636302948px;background-color:transparent;">a- </span><span
                              class="yiv6206190985"
                              id="yiv6206190985yui_3_16_0_1_1409745842588_6276"
style="font-size:10pt;background-color:transparent;">Chilled water
                              temperature and flow rate (chiller107)
                              ---->> Cold-side temperature and
                              flow rate (cold tank)</span><br>
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><span
                              id="yiv6206190985cb3df404-ecb5-41c5-84e7-c9df5231e498"
                              class="yiv6206190985GINGER_SOFTWARE_mark"><span
id="yiv6206190985c58ec2f8-fd5f-4984-bf91-203ebb3e56b5"
                                class="yiv6206190985GINGER_SOFTWARE_mark"><span
id="58f64090-63d7-4898-9fc8-714b8c5e5cc5"
                                  ginger_software_uiphraseguid="a3135635-4030-4d6b-b255-f316a9b4e30f"
                                  class="GINGER_SOFTWARE_mark">b</span></span></span>-
                            Temperature (and flow rate) to load (cold
                            tank) --->> Chilled water inlet temp
                            and flow rate (chiller) trough a constant
                            speed pump</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><span
                              id="yiv6206190985ce65c357-e3c2-455a-9a6b-54e7475c3d8d"
                              class="yiv6206190985GINGER_SOFTWARE_mark"
                              style="font-size:10pt;"><span
                                id="yiv6206190985122dba59-0ced-4ab2-aeae-5c40a18c083a"
class="yiv6206190985GINGER_SOFTWARE_mark"><span
                                  id="4308a211-2d03-4f7d-a580-7cf07c4f48b8"
ginger_software_uiphraseguid="f20d83ad-c65e-4803-9521-3b18a6f9e01a"
                                  class="GINGER_SOFTWARE_mark">c</span></span></span><span
                              style="font-size:10pt;"
                              id="yiv6206190985yui_3_16_0_1_1409773050248_4207">-
                              Outlet temperature and flow rate (type
                              682) --->> Hot-side temperature and
                              flow rate (cold tank) through a pump</span><br>
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><span
                              id="yiv6206190985f19ff-4912-4c19-93e5-ac007df4293e"
                              class="yiv6206190985GINGER_SOFTWARE_mark"><span
id="yiv62061909853099ac69-70a9-4936-b78a-62527f405976"
                                class="yiv6206190985GINGER_SOFTWARE_mark"><span
id="5a82e45d-6157-416e-8843-2bc577fbc0f6"
                                  ginger_software_uiphraseguid="0de4177e-2748-4de3-8679-2c51642e703e"
                                  class="GINGER_SOFTWARE_mark">d</span></span></span>-
                            Temperature (and flow rate) to heat source
                            (cold tank) --->> Inlet temperature
                            and flow rate of type 682</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><span
                              style="font-size:10pt;"
                              id="yiv6206190985yui_3_16_0_6_1409773050248_37"><br>
                            </span></div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><span
                              style="font-size:10pt;"
                              id="yiv6206190985yui_3_16_0_6_1409745842588_406">Am
                              I right? If yes, a</span><span
                              style="font-size:10pt;"
                              id="yiv6206190985yui_3_16_0_1_1409745842588_14117">re
                              there other reasons, such as the set point
                              temp of the Aux heater, that might cause
                              this error?</span></div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><br>
                          </div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style="">Kind regards,</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style="">Shahen</div>
                          <div
                            id="yiv6206190985yui_3_16_0_6_1409745842588_8"
                            class="yiv6206190985" style=""><br>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>