<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Martin,<br>
      One convenient way of defining the solar fraction is: <br>
    <br>
    qDelivered/(qAux + qParasitics)<br>
    <br>
    qDelivered would come from your adsorption chiller model, qAux would
    be the amount of energy delivered by the aux heater, and qParasitics
    would primarily be your pumping energy and the electricity required
    by the adsorption chiller. This method avoids having to worry at all
    about what is happening in the tank.<br>
    Kind regards,<br>
     David<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 5/3/2014 05:23, Martin Berov wrote:<br>
    </div>
    <blockquote
cite="mid:CAJam3+WEg7Zu5OxOUjrpULX+UPWW85d5TQd3Xr2j5oRR5qCUog@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi to all,
        <div><br>
        </div>
        <div>I need opinion about a calculation: I have a tank Type 60
          which is heated with solar collectors(heat exchanger) and it's
          outlet is in serial connected to auxiliary heater used to
          drive adsorption chiller. The return of the chiller is sent
          either in the tank or  again directly to the aux.heater
          depending from the temperature etc...</div>
        <div>Since I want to calculate the solar fraction I need the
          amount of energy removed from the tank so do you think than I
          only need the output "Energy removed from the outlet" or I
          need the difference between the "Energy removed from the
          outlet - Energy supplied from the inlet" - since if I use this
          difference I never reach the required heat energy - For
          example having adsorption chiller with 5 kW cooling power even
          with aux heater of 30 kW and flow rate of 5000 kg/h I have hot
          energy lower than the required? </div>
        <div>I also use the heat, cooling and chilled energy in the
          control strategy</div>
        <div><br>
        </div>
        <div>What do you think?</div>
        <div><br>
        </div>
        <div>Kind regards</div>
        <div>Martin</div>
        <div><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>