    Martin,<br>
      You are correct; Type107 is designed so that it takes the chilled
    water set point as an input and provides the required power as an
    output. If you are working on a simulation where you have a certain
    amount of power available (from a PV or a wind turbine) then what
    you can do is to implement two instances of Type107 in your
    simulation. One of them would be running all the time (i.e. it's
    control signal input is always set to 1) with its cooling water, hot
    water, and chilled water inputs connected but none of its outputs
    connected. The only output that you would use would be the required
    power. This instance of Type107 would be in your simulation only to
    determine how much power would be required in order to run an
    absorption chiller under current conditions. The required power
    would feed into an equation that would compare the required power to
    the power that you actually have available. If you have more power
    than you need then the equation's value would be 1. If you don't
    have enough power to run the chiller then the equation's value would
    be 0. The result of the equation would be sent as the control signal
    to a second instance of Type107 that is identical to the first
    except that it is not always on and its outputs (the outlet cooling
    water, chilled water, and hot water outlet conditions) are
    connected.<br>
      In essence you are using a virtual chiller to determine a control
    signal for the actual chiller. <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/25/2014 04:17, Martin Berov wrote:<br>
    </div>
    <blockquote
cite="mid:CAJam3+W7BMa34B=3FYhXo6ZB01GOwcU12NZv4ncCG7vpSJSMTg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Thank you, I found the weather block it was in the
        hidden layer.
        <div>I have one more issue, as I understand the absorption
          chiller always modulate its power so it can reach the chilled
          water set point temperature? - so does it mean that with this
          type 107 it is not possible to make simulations with different
          chiller powers(rated capacity) and see how they affect on the
          system? </div>
        <div><br>
        </div>
        <div>Kind regards</div>
        <div>Martin</div>
        <div><br>
        </div>
        <div><br>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Fri, Apr 25, 2014 at 2:48 AM, Jeremy
          Osborne <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:jeremy.osborne@solem-consulting.com"
              target="_blank">jeremy.osborne@solem-consulting.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div link="#0563C1" vlink="#954F72" lang="EN-GB">
              <div>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Hi
                    Martin, </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">The
                    weather data is hidden in a layer. Go to view ->
                    show layers -> and enable weather - data files
                    and you should see TYPE15-2 appear with all the
                    connection. </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Layers
                    are used to better organise complex models, removing
                    certain clutter. </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Regards,<br>
                    Jeremy </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                      lang="EN-US">SOLEM Consulting Pty Ltd</span></b><span
style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">Jeremy Osborne | Project Engineer BE </span><span
style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-US">525 Harris St | SYDNEY NSW 2007|
                    Australia</span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">P:  <a moz-do-not-send="true"
                      href="tel:%2B61%202%208006%207355"
                      value="+61280067355" target="_blank">+61 2 8006
                      7355</a></span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">M: <a moz-do-not-send="true"
                      href="tel:%2B61%20421%20914%20516"
                      value="+61421914516" target="_blank">+61 421 914
                      516</a></span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">E: </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
                    lang="EN-AU"><a moz-do-not-send="true"
                      href="mailto:jeremy.osborne@solem-consulting.com"
                      target="_blank"><span
                        style="font-size:10.0pt;color:blue">jeremy.osborne@solem-consulting.com</span></a></span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU"> </span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">W: </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
                    lang="EN-AU"><a moz-do-not-send="true"
                      href="http://www.solem-consulting.com/"
                      target="_blank"><span
                        style="font-size:10.0pt;color:blue">www.solem-consulting.com</span></a></span></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU">Follow our useful updates: <a
                      moz-do-not-send="true"
                      href="http://www.linkedin.com/company/solem-consulting"
                      target="_blank"><span style="color:blue">linkedin.com/company/solem-consulting</span></a></span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
                    lang="EN-AU"> </span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"> </span></p>
                <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#76923c"
                    lang="EN-AU">Please consider the environment before
                    printing this email </span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-AU"> </span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
                    lang="EN-AU">PLEASE NOTE</span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
                    lang="EN-AU"> </span><span
                    style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
                    lang="EN-AU">The information contained in this
                    e-mail may be confidential or privileged. Any
                    unauthorised use or disclosure is prohibited. If you
                    have received this e-mail in error, please delete it
                    immediately and notify the sender by return email.
                    Thank you. To the extent permitted by law, Solem
                    Consulting does not represent, warrant and/or
                    guarantee the integrity of this communication has
                    been maintained nor the communication is free of
                    error, virus, interception or interference.</span><span
style="font-family:"Arial","sans-serif""
                    lang="EN-AU"></span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
                <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif""
                      lang="EN-US">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif""
                    lang="EN-US"> Martin Berov [mailto:<a
                      moz-do-not-send="true"
                      href="mailto:martber88@gmail.com" target="_blank">martber88@gmail.com</a>]
                    <br>
                    <b>Sent:</b> Thursday, 24 April 2014 8:02 PM<br>
                    <b>To:</b> <a moz-do-not-send="true"
                      href="mailto:trnsys-users@cae.wisc.edu"
                      target="_blank">trnsys-users@cae.wisc.edu</a><br>
                    <b>Subject:</b> [TRNSYS-users] Restaurant absorp.
                    cooling Tess example</span></p>
                <div>
                  <div class="h5">
                    <p class="MsoNormal"> </p>
                    <div>
                      <p class="MsoNormal">Hi,</p>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">I was looking at the
                          example provided  with the Tess library about
                          the Restaurant absorption chilling, so the
                          simulation runs ok, but I can not find the
                          weather block i.e. the collector and building
                          are not connected to it -how is this possible,
                          how does it function, can someone give me
                          explanation?</p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">Thank you</p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">Best Regards</p>
                      </div>
                      <div>
                        <p class="MsoNormal">Martin</p>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>