<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Tilak,<br>
      If the comparisons are simple then you may be able to use
    equations in the input file to determine how much power needs to go
    to meet the load or run the electrolyzer. If they get more complex
    then there are some master controller components available in the
    Hydrogen Systems directory (look first at Type105). Bear in mind
    that these are quite generic controllers. In all of the cases that I
    have had to deal with, I needed to write my own controller model
    using a Fortran compiler because there were some special
    requirements on the controls (for example what do you do if the load
    cannot be met by PV and the state of charge in the hydrogen tank is
    so low that you cannot run the fuel cell either.<br>
    <br>
      Also as a side note, keep in mind that electrolyzers have a fairly
    significant standby power requirement. This would be some power that
    they draw when idle so that when excess electricity becomes
    available, the hydrogen produced is pure enough to be useful. There
    are also systems in which the electrolyzer is shut down (instead of
    allowed to idle) but in these cases the hydrogen that they produce
    while being started up is not useful. This is another reason why you
    might need to write your own master controller component.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 4/12/2014 17:29, Tilak Sunwar wrote:<br>
    </div>
    <blockquote
cite="mid:CAF9knayLZEQKeGmn-xfHQmQnHOtKp2NCQGPLTm-xBwYJCX+Tcw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi David,
        <div><br>
        </div>
        <div>I am currently doing a Miner Thesis project as part of my
          Master course. I am designing a Solar PV-Thermal and Hydrogen
          system for heat and power. I am looking for a LOAD SPLITTER
          which should perform the following </div>
        <div>1. First compare the PV power and the load demand at that
          particular hour.</div>
        <div>2. If the load is less than or equal to PV power generated,
          than the supply the power to Load only.</div>
        <div>3. If there is excess power from the PV, supply to
          electrolizer to generate hydrogen.</div>
        <div>4. Hydrogen will be utilize when there is no solar
          radiation.</div>
        <div><br>
        </div>
        <div>I would highly appreciate if you could provide me your
          guidance in the above area mentioned,</div>
        <div><br>
        </div>
        <div>Looking forward to your kind response.</div>
        <div><br>
        </div>
        <div>Thanks</div>
        <div>Tilak<br>
          -- <br>
          <div dir="ltr">
            <div> </div>
            <div><span style="color:rgb(51,51,51);font-family:'lucida
                grande',tahoma,verdana,arial,sans-serif;line-height:17px">"Wisdom
                you don’t get in colleges, schools, universities,
                nowhere. Where do you get it, the wisdom? You get it
                through your spirit, which gives you a complete idea as
                to what is right and what is wrong."</span><br
                style="color:rgb(51,51,51);font-family:'lucida
                grande',tahoma,verdana,arial,sans-serif;line-height:17px">
              <span style="color:rgb(51,51,51);font-family:'lucida
                grande',tahoma,verdana,arial,sans-serif;line-height:17px">H.H
                Shri Mataji Nirmala Devi, </span><span
                style="color:rgb(51,51,51);font-family:'lucida
                grande',tahoma,verdana,arial,sans-serif;line-height:17px">August
                28,1994, Cabella, Italy</span><br
                style="color:rgb(51,51,51);font-family:'lucida
                grande',tahoma,verdana,arial,sans-serif;line-height:17px">
              <br>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>