    Metkel,<br>
      Control signals in TRNSYS are almost always a value between 0
    (off) and 1 (on) and you can write equations using Boolean logic to
    set them. For example, if you define a variable called Tambient then
    you could write an equation such as:<br>
    <br>
    yHeat = LT(Tambient,14)<br>
    <br>
    the variable yHeat would have a value of 1 as long as the variable
    Tambient was less than 14. You can also use the same idea to set
    multipliers on input or output data. For example, if your Type9 is
    simply reading a value of load without any indication of whether it
    is a heating load or a cooling load then you could write the
    following two equations:<br>
    <br>
    heatLoad = Type9output*LT(Tambient,14)<br>
    coolLoad = Type9output*GT(Tambient,18)<br>
    <br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2/6/2014 06:02, metkell yebiyo
      wrote:<br>
    </div>
    <blockquote
      cite="mid:1391688176.2136.YahooMailNeo@web173104.mail.ir2.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff;
        font-family:HelveticaNeue, Helvetica Neue, Helvetica, Arial,
        Lucida Grande, Sans-Serif;font-size:12pt">
        <div>Dear TRNSYS users,</div>
        <div><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">My name is
          Metkel, I am a researcher at London South Bank University, I
          am currently trying to simulate a GSHP system. the GSHP is
          controlled by the outside temperature, if the outside
          temperature is less than 14 then a control signal  tells the
          GSHP to run in heating mode, if the outside temp is greater
          than 18 then the control signal tells the GSHP to run in
          cooling mode.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">However I
          couldn't figure out how to write the equation to the following
          please.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">1. based
          on the outside temperature to send a signal to the heat pump.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">2. based
          on the outside temperature to retrieve the cooling or heating
          load of the building from</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">    type
          9a which contains the building load.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">3. based
          on the outside temperature to also send a signal to the
          circulation pumps to switch them</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">   on or
          off accordingly.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">Any
          suggestions would be much appreciated please.</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">Regards,</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;">Metkel</div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
        <div style="color: rgb(0, 0, 0); font-size:
          16.363636016845703px; font-family: HelveticaNeue, 'Helvetica
          Neue', Helvetica, Arial, 'Lucida Grande', sans-serif;
          background-color: transparent; font-style: normal;"><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>