    Ryan,<br>
      There are (at least) two ways that you can approach this. One way
    is to write some equations using Boolean functions that enable and
    disable the economizer and chiller based on ambient temperature.
    Please see my response earlier today to a post called "Control
    signal for GSHP" to some tips on setting these equations. <br>
    <br>
      It is slightly different from the control logic you describe but
    you could also make use of the multi stage cooling ability in the
    Type108 thermostat model. You could use this model to enable the
    economizer if the zone temperature gets to a certain temperature but
    then turn off the economizer and turn on the chiller if the room
    temperature continues to rise to a second setpoint temperature.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2/7/2014 04:06, Jian Yan wrote:<br>
    </div>
    <blockquote cite="mid:COL128-W74DBAA5836CDABA95D152AD970@phx.gbl"
      type="cite">
      <div dir="ltr">
        <div dir="ltr">
          <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
          <div dir="ltr">
            <div>Hello dears,</div>
            <div><br>
            </div>
            <div>I'm recently building a thermal model of a server room
              in TRNSYS 17, where two types of cooling systems are
              applied, chiller and economizer. My goal is to cool the
              server room by the chiller when the ambient temperature is
              above 18 centigrade, while using free cooling (economizer)
              when the temperature is below 18 centigrade. </div>
            <div><br>
            </div>
            <div>The chiller system is already built and functional,
              however, I have no clue how to enable the model switch
              between the two cooling systems automatically according to
              the outdoor temperature, like how to set the temperature
              sensor, valve or other staffs.</div>
            <div><br>
            </div>
            <div>Thank you very much in advance.</div>
            <div><br>
            </div>
            <div>Best regards,</div>
            <div>Ryan</div>
            <div><br>
            </div>
            <iframe id="tmp_downloadhelper_iframe" style="display:
              none;"></iframe></div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>