<html><body bgcolor="#FFFFFF"><div>That being said, even with those programs, the modelling of airflow through large horizontal openings is "rough" at best. CFD may be a helpful tool to gain insights here.<br><br><div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.28125); -webkit-composition-fill-color: rgba(175, 192, 227, 0.214844); -webkit-composition-frame-color: rgba(77, 128, 180, 0.214844); ">Mit freundlichen Grüßen- Sent from my iPhone <span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.273438); -webkit-composition-fill-color: rgba(175, 192, 227, 0.207031); -webkit-composition-frame-color: rgba(77, 128, 180, 0.207031); ">(excuse the brevity)</span></span></div><div><br></div><div>i. A.</div><div>Jean Marais</div><div>b.i.g. bechtold</div><div>Tel.   +49 30 6706662-23</div></div><div><br>On 14.02.2014, at 22:31, David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>
    Karol,<br>
      What I have often done is to define a coupling air flow between
    the two zones, then run the simulation once with very little
    coupling flow and then once with a high airflow. The values of "low"
    and "high" are somewhat arbitrary; the idea is to make a reasonable
    guess as to how much air transfer there is. If there is no real
    difference in the simulation outputs that I care about (such as
    comfort or total building energy consumption) then I am confident
    that I don't have to spend much time thinking about what a good
    value would be (the model isn't sensitive to the value). If I find
    that there is a high degree of sensitivity then I can focus some
    more effort there.<br>
    <br>
      At the other end of the spectrum, you can of course implement
    COMIS, CONTAM, or TRNFlow in the building so as to get an estimate
    of what the transfer might be.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 2/14/2014 12:26, Karol Bandurski
      wrote:<br>
    </div>
    <blockquote cite="mid:00b901cf29b2$551dd650$ff5982f0$@put.poznan.pl" type="cite">
      
      
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Tekst dymka Znak";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        mso-fareast-language:EN-US;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0cm;
        margin-right:0cm;
        margin-bottom:0cm;
        margin-left:36.0pt;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";
        mso-fareast-language:EN-US;}
span.Stylwiadomocie-mail18
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.Stylwiadomocie-mail19
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.TekstdymkaZnak
        {mso-style-name:"Tekst dymka Znak";
        mso-style-priority:99;
        mso-style-link:"Tekst dymka";
        font-family:"Tahoma","sans-serif";
        mso-fareast-language:EN-US;}
span.Stylwiadomocie-mail22
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:1639410485;
        mso-list-type:hybrid;
        mso-list-template-ids:1398710632 67567631 67567641 67567643 67567631 67567641 67567643 67567631 67567641 67567643;}
@list l0:level1
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l0:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l0:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-18.0pt;}
@list l0:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
ol
        {margin-bottom:0cm;}
ul
        {margin-bottom:0cm;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color:#1F497D">Dear Jochen,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Thank
            you for your advice, but now I am looking for the values for
            such exchange, and the basis for this airflow assumption.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">What
            is your practice with this issue?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Regards,<br>
            Karol<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";mso-fareast-language:PL">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";mso-fareast-language:PL">
                hotline [<a class="moz-txt-link-freetext" href="mailto:hotline@Transsolar.com"><a href="mailto:hotline@Transsolar.com">mailto:hotline@Transsolar.com</a></a>] <br>
                <b>Sent:</b> Friday, February 14, 2014 4:48 PM<br>
                <b>To:</b> 'TRNSYS users mailing list at the Solar
                Energy Lab, UW-Madison'<br>
                <b>Subject:</b> Re: [TRNSYS-users] air contact<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="DE">Dear
            Karol,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="DE"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">You
            can merge both zones to one zone and two airnodes. Please
            have a look into the manual 5.4.1 for the difference between
            airnode and zone. </span><span lang="EN-US"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoListParagraph" style="text-indent:-18.0pt;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span style="color:#1F497D" lang="EN-US"><span style="mso-list:Ignore">1.<span style="font:7.0pt
                "Times New Roman"">       </span></span></span><!--[endif]--><span style="color:#1F497D" lang="EN-US">if you draw the building
            in SketchUp, you need to define the wall as a virtual
            surface, to merge them in TRNBuild ,use the 180° arrow on
            the upper left site of the zone window<o:p></o:p></span></p>
        <p class="MsoListParagraph" style="text-indent:-18.0pt;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span style="color:#1F497D" lang="EN-US"><span style="mso-list:Ignore">2.<span style="font:7.0pt
                "Times New Roman"">       </span></span></span><!--[endif]--><span style="color:#1F497D" lang="EN-US">If you define the wall
            manually in TRNBuild ,you can add directly another airnode
            to the zone.  <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"> <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">After
            merging you have two airnodes in the zone and you might need
            to define an air exchange see 5.2.4.10.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US">Best<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D" lang="EN-US"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><i><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="EN-US">__________________________________________________________________________________________________<o:p></o:p></span></i></p>
          <p class="MsoNormal"><i><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="EN-US"><o:p> </o:p></span></i></p>
          <p class="MsoNormal"><i><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">Jochen Lam<o:p></o:p></span></i></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">TRNSYS Software Team<o:p></o:p></span></p>
          <p class="MsoNormal"><i><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE"><br>
              </span></i><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">Transsolar Energietechnik GmbH<o:p></o:p></span></b></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">Curiestraße 2<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">70563 Stuttgart<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">Fax:        +49 711 67976-11<br>
              Email:    <a moz-do-not-send="true" href="mailto:jlam@transsolar.com"><a href="mailto:jlam@transsolar.com">jlam@transsolar.com</a></a><o:p></o:p></span></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:black;mso-fareast-language:DE" lang="DE">Web:      <a moz-do-not-send="true" href="http://www.trnsys.de"><a href="http://www.trnsys.de">www.trnsys.de</a></a> </span><span style="color:#1F497D;mso-fareast-language:DE" lang="DE"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D" lang="DE"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";mso-fareast-language:DE" lang="DE">Von:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";mso-fareast-language:DE" lang="DE"> <a moz-do-not-send="true" href="mailto:trnsys-users-bounces@cae.wisc.edu"><a href="mailto:trnsys-users-bounces@cae.wisc.edu">trnsys-users-bounces@cae.wisc.edu</a></a>
                [<a moz-do-not-send="true" href="mailto:trnsys-users-bounces@cae.wisc.edu"><a href="mailto:trnsys-users-bounces@cae.wisc.edu">mailto:trnsys-users-bounces@cae.wisc.edu</a></a>]
                <b>Im Auftrag von </b>Karol Bandurski<br>
                <b>Gesendet:</b> Freitag, 14. Februar 2014 15:24<br>
                <b>An:</b> <a moz-do-not-send="true" href="mailto:trnsys-users@cae.wisc.edu"><a href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a></a><br>
                <b>Betreff:</b> [TRNSYS-users] air contact<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><span lang="DE"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Dear All,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I wondering how are you
            model air contact:<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">there is two zones (e.g.
            two rooms) and they are connected by air (e.g. doorway),
            there are no mechanical ventilation or intensive, one
            direction, air flow.<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">I think to assume some
            massless construction between this zones, but what
            resistance will be appropriate? Or maybe some both direction
            air flow, but how can I assume the value of the flow?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Do you have some idea?<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Kind regards,<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US">Karol<o:p></o:p></span></p>
        <p class="MsoNormal"><span lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:PL" lang="EN-US">------------------------------------------------<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="mso-fareast-language:PL" lang="EN-US">Karol Bandurski MSc.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="background:white;mso-fareast-language:PL"><a moz-do-not-send="true" href="http://www.ee.put.poznan.pl/" target="_top"><span style="color:windowtext;text-decoration:none" lang="EN-US">Institute of Environmental Engineering</span></a></span><span style="background:white;mso-fareast-language:PL" lang="EN-US"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="background:white;mso-fareast-language:PL" lang="EN-US">Poznan University of Technology<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="background:white;mso-fareast-language:PL" lang="EN-US"><a moz-do-not-send="true" href="http://www.put.poznan.pl/%7Ekarol.bandurski"><a href="http://www.put.poznan.pl/~karol.bandurski">www.put.poznan.pl/~karol.bandurski</a></a><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="background:white;mso-fareast-language:PL"><a moz-do-not-send="true" href="http://www.ee.put.poznan.pl"><a href="http://www.ee.put.poznan.pl">www.ee.put.poznan.pl</a></a><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu"><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com"><a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a></a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com"><a href="http://www.tess-inc.com">http://www.tess-inc.com</a></a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com"><a href="http://www.trnsys.com">http://www.trnsys.com</a></a></pre>
  

</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>TRNSYS-users mailing list</span><br><span><a href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a></span><br><span><a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a></span><br></div></blockquote></body></html>