<div dir="ltr"><div><div><br></div>Carol,<br><br>I forgot one more thing: make sure that the output control function is connected to the same type "input control function", cheers<br><br></div>Angel<br></div><div class="gmail_extra">
<br><br><div class="gmail_quote">2014/1/24 Angel Carrera <span dir="ltr"><<a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a>></span><br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr"><div><div><div><div><div><div><br></div>Egun on Carol,<br><br></div>I think there a two basic reasons for this:<br><br></div>1-The controller gets stuck due to a lack of stability of your model. Parameter 1 sets the number of oscillations that the controller can do in a single time step; if the controller changes of state while trnsys is iterating within a time step, it will never do it (change) more times than the value you have set in parameter 1, so it gets fixed when the number of changes reaches that value. I can't explain it better than it is done in the user help (at least in english), so I recommend you to carefully read the introduction in the controllers section of the mathematical reference on the trnsys help as well as type 2b section. To solve this, usually the best you can do is reduce you time step until you have a coherent behaviour of the controller.<br>

<br></div>2-The monitoring temperature is governing the controller. If the Input Control Functio (inputs tab of the proforma) exceeds the value of the parameter 2, then the controller output is set to 0. <br><br></div>I imagine that the first possibility is the one explaining that behaviour; reducing the time step is probably a good help for your model, good luck<br>

<br></div>Angel<br></div><div class="gmail_extra"><br><br><div class="gmail_quote">2014/1/24 Pascual Ortiz, Carol <span dir="ltr"><<a href="mailto:carol.pascual@tecnalia.com" target="_blank">carol.pascual@tecnalia.com</a>></span><br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5">





<div link="blue" vlink="purple" lang="EN-GB">
<div>
<p class="MsoNormal">Hi TRNSYS user,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">In my last simulation I use type 2 on/off differential controllers and I do not know why sometimes it works ok and others doesn´t.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">For example Time step                temperature                       control  signal<u></u><u></u></p>
<p class="MsoNormal">                                4016,65                     25                                                  0<u></u><u></u></p>
<p class="MsoNormal">                                4016,70                     25                                                  1<u></u><u></u></p>
<p class="MsoNormal">                                4016,75                     25                                                  0<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Do you know what I am doing wrong? Does this ever happen to you?<u></u><u></u></p>
<p class="MsoNormal">Thank you in advance, <u></u><u></u></p>
<p class="MsoNormal">Best regards,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" style="vertical-align:baseline"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="ES">Carol Pascual</span></b><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="ES">Energía Térmica/Thermal Energy
</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u><u></u></span></p>
<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u> <u></u></span></p>
<p class="MsoNormal" style="vertical-align:baseline"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#c75b12" lang="ES">División de Energía y Medio Ambiente/<u></u><u></u></span></b></p>


<p class="MsoNormal" style="vertical-align:baseline"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#c75b12" lang="ES">Energy and Environment Division<u></u><u></u></span></b></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u> <u></u></span></p>
<p class="MsoNormal" style="vertical-align:baseline"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="ES">TECNALIA</span></b><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="PT-BR">Área Anardi,5</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="PT-BR">Laida Bidea, Edificio 204</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="ES"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="PT-BR">E-20730 Azpeitia - Gipuzkoa (Spain)</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif""><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="EN-US">T 902 760 000*<u></u><u></u></span></p>
<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357">M 667119581</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif""><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="EN-US">T <a href="tel:%2B34%20946%20430%20850" value="+34946430850" target="_blank">+34 946 430 850</a> (International calls)</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="EN-US"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="ES"><a href="mailto:carol.pascual@tecnalia.com" target="_blank"><span style="color:blue" lang="EN-US">carol.pascual@tecnalia.com</span></a></span><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="EN-US"><u></u><u></u></span></p>


<p class="MsoNormal" style="vertical-align:baseline"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4d5357" lang="EN-US"><a href="http://www.tecnalia.com/" target="_blank"><span style="color:blue">www.tecnalia.com</span></a></span><span style="font-size:12.0pt;font-family:"Times New Roman","serif"" lang="EN-US"><u></u><u></u></span></p>


<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>

<br></div></div>_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br><font style="color:rgb(0,102,0)" size="4"><b>Àngel Carrera</b></font><br style="color:rgb(0,102,0)"><br style="color:rgb(0,102,0)"><b style="color:rgb(0,102,0)">Consultor Senior<br>

Àrea
 tècnica</b><br style="color:rgb(0,102,0)"><img src="http://www.aiguasol.coop/img/logo.gif"><br><span style="color:rgb(0,153,0)">Sistemes Avançats d'Energia Solar 
Tèrmica SCCL</span><br style="color:rgb(0,153,0)">
<span style="color:rgb(0,153,0)">C/ Roger de Llúria, 29 3r 2a 08009 
Barcelona</span><br><span style="color:rgb(0,153,0)">Mòbil</span>: <span style="color:rgb(0,153,0)"><a href="tel:%28%2B34%29%20663%2027%2066%2080" value="+34663276680" target="_blank">(+34) 663 27 66 80</a></span><br style="color:rgb(0,153,0)">
<span style="color:rgb(0,153,0)">Tel: <a href="tel:%28%2B34%29%2093%20342%2047%2055" value="+34933424755" target="_blank">(+34) 93 342 47 55</a><br>Fax: <a href="tel:%28%2B34%29%2093%20342%2047%2056" value="+34933424756" target="_blank">(+34) 93 342 47 56</a></span><br>

<font color="#888888"><br>
<a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a><br><a href="http://www.aiguasol.coop/" target="_blank">http://www.aiguasol.coop</a></font>
</div>
</blockquote></div><br><br clear="all"><br>-- <br><font style="color:rgb(0,102,0)" size="4"><b>Àngel Carrera</b></font><br style="color:rgb(0,102,0)"><br style="color:rgb(0,102,0)"><b style="color:rgb(0,102,0)">Consultor Senior<br>
Àrea
 tècnica</b><br style="color:rgb(0,102,0)"><img src="http://www.aiguasol.coop/img/logo.gif"><br><span style="color:rgb(0,153,0)">Sistemes Avançats d'Energia Solar 
Tèrmica SCCL</span><br style="color:rgb(0,153,0)">
<span style="color:rgb(0,153,0)">C/ Roger de Llúria, 29 3r 2a 08009 
Barcelona</span><br><span style="color:rgb(0,153,0)">Mòbil</span>: <span style="color:rgb(0,153,0)">(+34) 663 27 66 80</span><br style="color:rgb(0,153,0)"><span style="color:rgb(0,153,0)">Tel: (+34) 93 342 47 55<br>Fax: (+34) 93 342 47 56</span><br>
<font color="#888888"><br>
<a href="mailto:angel.carrera@aiguasol.coop" target="_blank">angel.carrera@aiguasol.coop</a><br><a href="http://www.aiguasol.coop/" target="_blank">http://www.aiguasol.coop</a></font>
</div>