<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Ali, <br>
      You need to decide what device you want to use to deliver the
    cooling to the zone. An absorption chiller generates cold water so
    you can use that cold water in a fan coil or (perhaps) in a radiant
    panel. If you are using fan coils then you would define a
    VENTILATION type in TRNBuild/Type56 that is going to be the air
    (temperature, RH, and flow rate) coming from the fan coil model.
    You'll connect the fan coil model to pipe models, to a pump model
    and then to the absorption chiller model. I would highly recommend
    that you follow the tutorial called "Temperature Level Control from
    Energy Rate Control" located at:<br>
    <br>
<a class="moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm">http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm</a><br>
    <br>
    while the tutorial does not specifically deal with absorption
    chillers, the process is the same for connecting any kind of air
    distribution system to a building.<br>
    Regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 1/15/2014 00:46, ali javed wrote:<br>
    </div>
    <blockquote
cite="mid:CAKnBUf-UuLwTnwt1QeZMZoORLxJ1SftiuQ19odWF1OjGAYNfzA@mail.gmail.com"
      type="cite">
      <div dir="ltr">dear all <br>
        <br>
        i want to cool my building model developed in type 56 by using
        hot water fired single effect absorption chiller type 107 how
        can i connect these two type for cooling purpose ???</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>