Wang,<br>
Type28 is able to perform some manipulations on its inputs in
order to perform energy balances or unit conversions. The
manipulations are specified through a list of numeric codes that
appears in the third field of the "special cards" tab in the
proforma. The error that you are obtaining is saying that one of the
operation codes specifies that a manipulation should be performed on
an output that doesn't exist. For example, you would get this error
if the operation codes specify that the 5th output of component X
should be moved onto the stack but component X only has 4 outputs. <br>
<br>
I would strongly recommend that you not use Type28's ability to
perform these manipulations. It is very easy to make an error when
setting up a list of operation codes. Instead, I would recommend
that you use a block of equations to perform the unit conversions or
energy balances that you want, then pass the result of those
equations to a more standard output device (Type25 or Type46).<br>
Regards,<br>
David<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 12/9/2013 05:26, 王洋 wrote:<br>
</div>
<blockquote
cite="mid:CABF0dEt7ODwUrJU1Gewsv5Utte3Xg1DNE78U31rb78EBWTy4QA@mail.gmail.com"
type="cite">
<div dir="ltr">
<div>
<div>Dear all,<br>
<br>
</div>
Good Day!<br>
<br>
</div>
I met an error when I used Type 28 as follows.<br>
<div>
<div>
<div><br>
*** Notice at time : 0.100000<br>
Generated by Unit : 40<br>
Generated by Type : 28<br>
TRNSYS Message 446 : The maximum value from the
result of the supplied CHECK statement for this unit for
the simulation is shown below. A value of zero implies
that the energy balance was perfectly satisfied.<br>
Reported information : Maximum Error =
0.000000000000000E+000<br>
<br>
<br>
</div>
<div>Please see the attached deck file of this program.<br>
<br>
</div>
<div>Who had some experiences to deal with this problem?<br>
<br>
</div>
<div>Many thanks in advance!<br>
</div>
<div>Br.<br>
<br>
</div>
<div>yang wang <br>
</div>
<div> <br>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">2013/12/5 <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu"
target="_blank">trnsys-users-request@cae.wisc.edu</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">Send
TRNSYS-users mailing list submissions to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web,
visit<br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
or, via email, send a message with subject or body
'help' to<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-request@cae.wisc.edu">trnsys-users-request@cae.wisc.edu</a><br>
<br>
You can reach the person managing the list at<br>
<a moz-do-not-send="true"
href="mailto:trnsys-users-owner@cae.wisc.edu">trnsys-users-owner@cae.wisc.edu</a><br>
<br>
When replying, please edit your Subject line so it
is more specific<br>
than "Re: Contents of TRNSYS-users digest..."<br>
<br>
Today's Topics:<br>
<br>
1. Re: Workspace for TESS libraries (David
BRADLEY)<br>
2. Re: Workspace for TESS libraries (David
BRADLEY)<br>
3. Re: doors in sketchup /TRNbuild (David
BRADLEY)<br>
4. Re: CHILLER PERFORMANCE DATA (Jeremy Osborne)<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
To: "TRNSYS users mailing list at the Solar Energy
Lab, UW-Madison" <<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>>,
Trnsys discussion group <<a
moz-do-not-send="true"
href="mailto:trnsys-users@engr.wisc.edu">trnsys-users@engr.wisc.edu</a>>,
"<a moz-do-not-send="true"
href="mailto:a8304506@graduate.hku.hk">a8304506@graduate.hku.hk</a>"
<<a moz-do-not-send="true"
href="mailto:a8304506@graduate.hku.hk">a8304506@graduate.hku.hk</a>><br>
Cc: <br>
Date: Wed, 04 Dec 2013 16:17:25 -0600<br>
Subject: Re: [TRNSYS-users] Workspace for TESS
libraries<br>
Chun Kwong,<br>
We made the decision with the release of the v17
libraries not to distribute those workspaces. It was
hard to manage their settings and new versions of
the compiler continue to be released and are
challenging to manage. I would recommend that you
simply use the MyType project that is part of the
IVF11x solution. You can add as many Types to that
MyType project as you want.<br>
Kind regards,<br>
David<br>
<br>
<br>
On 12/3/2013 18:38, C K Lee wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">
Hello.<br>
<br>
I have previously installed TRNSYS 17 together
with the TESS libraries. However, unlike TRNSYS
16, I can't find where the workspace for the TESS
libraries is located. Does anyone know? If so,
please advise. Thank you!<br>
<br>
Best Regards<br>
LEE, Chun Kwong<br>
City University of Hong Kong<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu"
target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
<br>
-- <br>
***************************<br>
David BRADLEY<br>
Principal<br>
Thermal Energy Systems Specialists, LLC<br>
22 North Carroll Street - suite 370<br>
Madison, WI 53703 USA<br>
<br>
P:<a moz-do-not-send="true"
href="tel:%2B1.608.274.2577" value="+16082742577"
target="_blank">+1.608.274.2577</a><br>
F:<a moz-do-not-send="true"
href="tel:%2B1.608.278.1475" value="+16082781475"
target="_blank">+1.608.278.1475</a><br>
<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com"
target="_blank">d.bradley@tess-inc.com</a><br>
<br>
<a moz-do-not-send="true"
href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a><br>
<a moz-do-not-send="true"
href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a><br>
<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
To: "TRNSYS users mailing list at the Solar Energy
Lab, UW-Madison" <<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>>,
Trnsys discussion group <<a
moz-do-not-send="true"
href="mailto:trnsys-users@engr.wisc.edu">trnsys-users@engr.wisc.edu</a>>,
"<a moz-do-not-send="true"
href="mailto:a8304506@graduate.hku.hk">a8304506@graduate.hku.hk</a>"
<<a moz-do-not-send="true"
href="mailto:a8304506@graduate.hku.hk">a8304506@graduate.hku.hk</a>><br>
Cc: <br>
Date: Wed, 04 Dec 2013 16:17:25 -0600<br>
Subject: Re: [TRNSYS-users] Workspace for TESS
libraries<br>
Chun Kwong,<br>
We made the decision with the release of the v17
libraries not to distribute those workspaces. It was
hard to manage their settings and new versions of
the compiler continue to be released and are
challenging to manage. I would recommend that you
simply use the MyType project that is part of the
IVF11x solution. You can add as many Types to that
MyType project as you want.<br>
Kind regards,<br>
David<br>
<br>
<br>
On 12/3/2013 18:38, C K Lee wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">
Hello.<br>
<br>
I have previously installed TRNSYS 17 together
with the TESS libraries. However, unlike TRNSYS
16, I can't find where the workspace for the TESS
libraries is located. Does anyone know? If so,
please advise. Thank you!<br>
<br>
Best Regards<br>
LEE, Chun Kwong<br>
City University of Hong Kong<br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu"
target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
<br>
-- <br>
***************************<br>
David BRADLEY<br>
Principal<br>
Thermal Energy Systems Specialists, LLC<br>
22 North Carroll Street - suite 370<br>
Madison, WI 53703 USA<br>
<br>
P:<a moz-do-not-send="true"
href="tel:%2B1.608.274.2577" value="+16082742577"
target="_blank">+1.608.274.2577</a><br>
F:<a moz-do-not-send="true"
href="tel:%2B1.608.278.1475" value="+16082781475"
target="_blank">+1.608.278.1475</a><br>
<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com"
target="_blank">d.bradley@tess-inc.com</a><br>
<br>
<a moz-do-not-send="true"
href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a><br>
<a moz-do-not-send="true"
href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a><br>
<br>
<br>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: David BRADLEY <<a moz-do-not-send="true"
href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>><br>
To: "TRNSYS users mailing list at the Solar Energy
Lab, UW-Madison" <<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>>,
<a moz-do-not-send="true"
href="mailto:mohamed.khabbaz@gmail.com">mohamed.khabbaz@gmail.com</a><br>
Cc: <br>
Date: Wed, 04 Dec 2013 16:19:44 -0600<br>
Subject: Re: [TRNSYS-users] doors in sketchup
/TRNbuild<br>
<div bgcolor="#FFFFFF" text="#000000"> Mohamed,<br>
I would recommend that you treat glass doors as
windows in Trnsys3D (ie draw them in Trnsys3D but
set them to a different type of glass construction
then your windows so that it will be easier to
modify them later in TRNBuild). For opaque doors,
the easiest thing to do is to simply add them in
TRNBuild afterwards.<br>
Kind regards,<br>
David<br>
<br>
<br>
<div>On 12/4/2013 08:09, Mohamed Khabbaz wrote:<br>
</div>
<blockquote type="cite">
<div dir="ltr">
<div>Hi<br>
<br>
</div>
When I import my 3D model (.idf) from Sketchup
to TRNbuild, Trnbuild does not know doors and
glass doors ( But TRNbuild knows windows).<br>
<br>
<br>
what must I make to resolve this situation?<br>
<br>
Thank you in advance.<br>
<br clear="all">
Best regards.<br>
</div>
<br>
<fieldset></fieldset>
<br>
<pre>_______________________________________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@cae.wisc.edu" target="_blank">TRNSYS-users@cae.wisc.edu</a>
<a moz-do-not-send="true" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users" target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:<a moz-do-not-send="true" href="tel:%2B1.608.274.2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a moz-do-not-send="true" href="tel:%2B1.608.278.1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a moz-do-not-send="true" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a moz-do-not-send="true" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
</div>
<br>
<br>
---------- 已转发邮件 ----------<br>
From: "Jeremy Osborne" <<a moz-do-not-send="true"
href="mailto:jeremy.osborne@solem-consulting.com">jeremy.osborne@solem-consulting.com</a>><br>
To: "'LAHO DESIGN'" <<a moz-do-not-send="true"
href="mailto:lahodesign@yahoo.com">lahodesign@yahoo.com</a>>,
"'TRNSYS users mailing list at the Solar Energy Lab,
UW-Madison'" <<a moz-do-not-send="true"
href="mailto:trnsys-users@cae.wisc.edu">trnsys-users@cae.wisc.edu</a>><br>
Cc: <br>
Date: Thu, 5 Dec 2013 11:24:29 +1100<br>
Subject: Re: [TRNSYS-users] CHILLER PERFORMANCE DATA<br>
<div link="#0563C1" vlink="#954F72" lang="EN-GB">
<div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Dear
Laho</span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">There
are usually data files in the component file
(tmf) which can be edited for each instance
the chiller is used. Please see the picture
below. There is example files available for
the chiller usually and you can click edit.
Please see the component mathematical
reference for the type you require for the
details. </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">What
chiller kind (compression, absorption) are
you modelling? What trnsys type are you
wanting to use? </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">These
are important as the Fortran code underlying
the type is important to understand because
it times, the default method is not ideally
suited and needed modification. We’ve edited
the component to suit our needs and only use
two data files and shown in the image before
for a type 677 chiller from the TESS
extension. </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">If
you need further assistance do not hesitate
to contact us. </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><img
src="cid:part43.03040106.04070409@tess-inc.com"
height="193" width="539"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"></span></p>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-US">SOLEM Consulting Pty Ltd</span></b><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">Jeremy Osborne | Project
Engineer BE </span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-US">525 Harris St | SYDNEY NSW
2007| Australia</span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">P: <a moz-do-not-send="true"
href="tel:%2B61%202%208006%207355"
value="+61280067355" target="_blank">+61 2
8006 7355</a></span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">M: <a moz-do-not-send="true"
href="tel:%2B61%20421%20914%20516"
value="+61421914516" target="_blank">+61
421 914 516</a></span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">E: </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
lang="EN-AU"><a moz-do-not-send="true"
href="mailto:jeremy.osborne@solem-consulting.com"
target="_blank"><span
style="font-size:10.0pt;color:blue">jeremy.osborne@solem-consulting.com</span></a></span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU"> </span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">W: </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
lang="EN-AU"><a moz-do-not-send="true"
href="http://www.solem-consulting.com/"
target="_blank"><span
style="font-size:10.0pt;color:blue">www.solem-consulting.com</span></a></span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU">Useful updates: <a
moz-do-not-send="true"
href="http://www.linkedin.com/company/solem-consulting"
target="_blank"><span style="color:blue">http://www.linkedin.com/company/solem-consulting</span></a></span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#1f497d"
lang="EN-AU"> </span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"> </span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#76923c"
lang="EN-AU">Please consider the environment
before printing this email </span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif""
lang="EN-AU"> </span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
lang="EN-AU">PLEASE NOTE</span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
lang="EN-AU"> </span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#a6a6a6"
lang="EN-AU">The information contained in
this e-mail may be confidential or
privileged. Any unauthorised use or
disclosure is prohibited. If you have
received this e-mail in error, please delete
it immediately and notify the sender by
return email. Thank you. To the extent
permitted by law, Solem Consulting does not
represent, warrant and/or guarantee the
integrity of this communication has been
maintained nor the communication is free of
error, virus, interception or interference.</span><span
style="font-family:"Arial","sans-serif""
lang="EN-AU"></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> </span></p>
<div>
<div style="border:none;border-top:solid
#e1e1e1 1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif""
lang="EN-US">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif""
lang="EN-US"> LAHO DESIGN [mailto:<a
moz-do-not-send="true"
href="mailto:lahodesign@yahoo.com"
target="_blank">lahodesign@yahoo.com</a>]
<br>
<b>Sent:</b> Wednesday, 4 December 2013
9:15 PM<br>
<b>To:</b> <a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu"
target="_blank">TRNSYS-users@cae.wisc.edu</a><br>
<b>Subject:</b> [TRNSYS-users] CHILLER
PERFORMANCE DATA</span></p>
</div>
</div>
<p class="MsoNormal"> </p>
<div>
<div>
<p class="MsoNormal"
style="background:white"><span
style="font-family:"Helvetica","sans-serif"">HOW
CAN I MODIFY THE FILE WHICH CONTAINS THE
CHILLER PART LOAD PERFORMANCE DATA?</span></p>
</div>
<div>
<p class="MsoNormal"
style="background:white"><span
style="font-family:"Helvetica","sans-serif""> </span></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-family:"Helvetica","sans-serif"">THANKS</span></p>
</div>
</div>
</div>
</div>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a moz-do-not-send="true"
href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a><br>
<a moz-do-not-send="true"
href="https://mailman.cae.wisc.edu/listinfo/trnsys-users"
target="_blank">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a><br>
<br>
</blockquote>
</div>
<br>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>