Rémi,<br>
I am not sure that I entirely understand your configuration. I
would have approached this as a single zone (not three adjacent
zones) having its floor cut up into three parts. Each floor will be
imported into TRNBuild individually and can then be treated as
separate radiant floors. <br>
Kind regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 11/12/2013 07:18, Rémi Marconot
wrote:<br>
</div>
<blockquote
cite="mid:13816368.144489.1384262307231.JavaMail.www@wsfrf1115"
type="cite">
<p>Hello Trnsys users,</p>
<p> </p>
<p>By using Trnsys 3D with Google Sketchup, I would like to
simulate a 3 radiant floors system for a 800m² room. That is why
I have created with Google Sketchup, 3 adjacent zones which make
the entire floor in order to have 3 different active layers in
TrnBuild. However when I am running the simulation, an error
says that "adjacent wall not found".</p>
<p>How can I solve this problem or is there another solution
to create several active layers in a same surface to divide my
radiant floor ?</p>
<p>Thank you for any kind of help in advance.<br>
<br>
Rémi</p>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>