    Abhay,<br>
      There are a number of ways that you can handle this; the most
    appropriate one depends a bit on how you are modeling the chiller.
    If you are modeling an idealized chiller using a cooling type inside
    Type56/TRNBuild then you can schedule the COOLING Type's capacity
    using a schedule defined inside TRNBuild. If you are using an
    external chiller model such as the air or water cooled chiller from
    the TESS Libraries then you can use Type14 to define a forcing
    function that has a value of 1 between 7am and 4pm and a value of 0
    at other times. The output of the forcing function can then be used
    for your chiller control signal. I would caution you on running your
    chiller based only on the time of day. Typically chillers are run as
    needed in order to maintain a loop temperature (in other words based
    on a thermostat). If your chiller operates on both a thermostat and
    on a timer then you can combine two output signals by multiplying
    one by the other in an equation.<br>
    <br>
      It is also highly recommended that you follow through the tutorial
    in the Getting Started manual so that you get an understanding of
    the basic process of putting together a TRNSYS simulation.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 11/10/2013 23:55, Abhay Pratap Singh
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAEzQ2nkJAuSbrHQ8EcDqH1DAMDAxFZefR2zA4kvkxDJrVs4ccA@mail.gmail.com"
      type="cite">
      <div dir="ltr"><br clear="all">
        <div>hello users.</div>
        <div>i m a new users of trnsys. i m modelling type 56 building
          and do not know to give the schedule for chiller. my chiller
          is ON at 7 A.M. and OFF at 4 P.M. and it repeats every day. i
          hope you will help me out from this.</div>
        <div>thanks for any help.</div>
        <div dir="ltr"><br>
        </div>
        <div dir="ltr">With regards,
          <div>Abhay Pratap Singh</div>
          <div>MNIT, Jaipur</div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>