    <font color="#333333">Benoît,<br>
        I don't know whether you are trying to run an automatic
      optimization or not but the only solution I can think of is to
      make a series of buildings (*.b17 files) each with a variation of
      the wall in it. Put in an ASSIGN statement for each one of the
      *.b17 files and give each its own unique logical unit number. Then
      define a CONSTANT for the logical unit of the *.b17 file that
      Type56 will use. Then you can </font><font color="#333333"><font
        color="#333333">run a parametric study where you change the
        logical unit with each run.<br>
        Regards,<br>
         David<br>
        <br>
      </font></font>
    <div class="moz-cite-prefix"><br>
      <br>
      On 10/25/2013 08:03, benoit schmitt wrote:<br>
    </div>
    <blockquote
cite="mid:CABfK4kXHqWQCTHJ+0GNKBvRnnmAUvBT_mbtoG28khkEwUPs70g@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear All,
        <div><br>
        </div>
        <div>I'm looking for a method or a type, that can allow to
          change the U value of a wall or the conductivity of a layer as
          an Input (not the glazing one).'</div>
        <div><br>
        </div>
        <div>Actually, I need the mass of my wall layer and I can't put
          99% of the wall as a Windows<br clear="all">
          <div><br>
          </div>
          <div>Thanks in advance,</div>
          -- <br>
          <font color="#333333">Benoît SCHMITT<br>
          </font>
          <div>
            <div>Research Engineer</div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>