    Joshua,<br>
      Pumps typically set the flow rate for a loop based on their rated
    flow rate and the value of the input control signal. There are some
    pump models that will allow you to set the control signal to a value
    greater than 1 and therefore to exceed the pump's rated flow rate. I
    would recommend that you break your flow loop by removing one of the
    connections (the one that returns to the pump would be best). Then
    use an online plotter to look at the temperature and flow rate
    coming out of each component in the loop. Verify that you do not
    have any incorrect connections. Once you are convinced that there
    are no connection problems, reconnect the loop but disconnect
    whatever is connected to your pump's control signal. Force the
    control signal to be a known value either by setting a constant
    input value or by setting an equation. I think these tests will
    probably lead you to the problem.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/27/2013 09:47, Joshua Chia wrote:<br>
    </div>
    <blockquote
cite="mid:CADoQ9uh4B_LjLU5NrOahrFEnu894_EFUWz6-LVYXOPgz1otBnw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi
        <div><br>
        </div>
        <div>I'm trying to design a closed cycle hot water system for
          use with a Heat Exchanger with a Solar Collector, pump and
          tank. I want to be able to set the mass flow rate of the
          system but it seems that even though I've set the maximum flow
          rate in the pump, the actual flow rate is way higher than
          that. I'm guessing it is due to the tank. Can anyone help me
          out on what to do with the tank? I only want a simple tank
          with 1 inlet and 1 outlet and the mass flow rate to be the one
          i determine it to be.</div>
        <div><br>
        </div>
        <div>Many Thanks<br>
          <div>
            <div><br>
            </div>
            -- <br>
            <div dir="ltr">Regards</div>
            <div dir="ltr">Joshua</div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>