<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Marcus,<br>
      Make sure that you are using a short timestep (1-5 minutes) and
    that there is enough thermal capacitance in your flow loops. It may
    be that 10000 kg/h of air flowing through the device in the course
    of one time step is causing the system to be unstable. There was a
    recent post on this forum concerning a cooling tower connected to an
    absorption chiller that turned out to be exactly the same problem;
    far too much energy transferred in a system with far too little
    capacitance for the time step selected. The time step has to be
    shorter than the time constant of your system.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/15/2013 08:36, Marcus wrote:<br>
    </div>
    <blockquote
cite="mid:CAEzj1z4i778gOcb54Gq3vngejP=qDd0Fd-r3TACRX01m5cGQiA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>I am running type 1716. When I run with 1000 kg/hr flow, it
          simulates fine. When I increase to 10000, it causes
          psychometric SAT error  at -273K. <br>
          <br>
        </div>
        So far, I will use the wheel at 1/10 the flow, and then multiply
        after the wheel to get back to our design flow, just wondering
        if this is a known bug or I suppose the model isn't valid at
        such a flow rate? <br>
        <br>
        Cheers,<br>
        Marcus<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>