    Arnaud,<br>
      I assume that you are printing out the solar azimuth, solar
    zenith, and incidence angles for all of the surfaces of your
    building. If not, make sure that you do print them to your file and
    that you then reread those as well. Weather data does not have to
    come from Type15 unless you have selected the automatic radiation
    calculation option for your surfaces in TRNBuild. Make sure that all
    of your orientations in TRNBuild are set to the manual radiation
    mode (in which case you need to provide beam radiation on the
    surface, diffuse radiation on the surface, and incidence angle of
    beam radiation on the surface for every orientation.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 9/11/2013 10:21, Arnaud Candaele
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAKoCkGF411-=SLEYvPjDq1=b9f9PEnMxv==LhRJng3=EvB_1bQ@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>
          <div>
            <div>
              <div>
                <div>
                  <div>
                    <div>Hi everyone,<br>
                      <br>
                    </div>
                    I am trying to use the data from a .tm2 file for a
                    specific day, and create a new file that would
                    repeat that day several times.<br>
                    <br>
                  </div>
                  I read that this issue already had some answers, but
                  it still can't manage to do it. Here is what I do for
                  now :<br>
                </div>
                I used a system Printer (Type25a) to print in a file the
                data for that day (so data from the weather file, such
                as temperature, humidity, etc.. but also data coming
                from the "Radiation" and "AzimuthAngles" calculators
                that are automatically created when you initiate the
                project).<br>
                <br>
              </div>
              I then use a Type9c Data Reader to re-read the data of
              that day, and use it as an input for my building. It works
              fine for all the data except the data related to solar
              radiation and azimuth angle. I don't understand why,
              because it is exactly the same data as the one that is
              created automatically, but TRNSYS tells me that radiation
              data HAS to come from a type15 (weather file). <br>
              <br>
            </div>
            So, what could I do ?<br>
            <br>
          </div>
          Thanks for your help,<br>
          <br>
        </div>
        Arnaud.<br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>