<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Christian,<br>
      It sounds as though the connection from Type80 to Type56 is
    correct (in TRNBuild, you indicate that the outside convection
    coefficient for a wall should be an INPUT and you give the input a
    name such as HBACK3, then you connect some model to the new Type56
    input). You might need to have a look at the inputs to Type80,
    however. Type80 takes the surface temperature and the surrounding
    air temperature and computes a convective energy transfer
    coefficient so you would need to go back in to TRNBuild and add an
    output for the outside surface temperature of your wall, then pass
    the new Type56 output to Type80. You can repeat the process with
    multiple instances of Type80, one for each of your different
    surfaces.<br>
    <br>
      A word of caution, however! Type80 computes a convection
    coefficient based on that natural convection dominates. On outside
    surfaces, forced convection from the wind almost always dominates
    the heat transfer. You might be better served finding a correlation
    that computes a forced convection coefficient instead.<br>
    Best,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 8/23/2013 06:52, Brembilla Christian
      wrote:<br>
    </div>
    <blockquote
      cite="mid:D4453D734BEB3745966DAB67C967117F38E1A45D@EXMDB04.org.aalto.fi"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <style type="text/css" id="owaParaStyle"></style>
      <div style="direction: ltr;font-family: Tahoma;color:
        #000000;font-size: 10pt;">Dear All,
        <div><br>
        </div>
        <div>I have a problem with TYPE 80. I would like to see the <i>convective
            coefficient</i> <i>for</i> <b>back side</b> of surface
          change in time. </div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">I tried to set TYPE 80, I
            started in TRNBuild and I chose the INPUT <i>keyword </i>,
            HBACK3, then in Simulation studio I connected TYPE 80 <i>Convective
              coefficient for back side of surface </i>with TYPE 56
            HBACK3, and them I plot it.</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">When I run the simulation
            the convective coefficientfor <b>back side</b> starts from 0
            and it remains always constant at a about 9.5. I done the
            same thing with VERTICAL and the result does not change.</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div>I can set the <i style="font-size: 10pt;">convective
            coefficient</i><span style="font-size: 10pt;"> </span><i
            style="font-size: 10pt;">for</i><span style="font-size:
            10pt;"> </span><b style="font-size: 10pt;">front side </b><span
            style="font-size: 10pt;">of surface with TRNBuild chosing
            internal calculation.</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">Questions:</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">-someone could explain me
            how to use INPUT especially the difference between HBACK3
            and VERTICAL.</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">-how select a proper
            surface, for instance I would like to see the convective
            coefficient for the surface facing to the south, for the
            surface facing to the north and so on.</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">Regards</span></div>
        <div><span style="font-size: 10pt;"><br>
          </span></div>
        <div><span style="font-size: 10pt;">Christian</span></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>